How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
Answer / ravi patel
Plug setting of a relay is the setting of a relay pick up current.
A relay pick up current is defined as the value of current through relay coil at which relay starts to operate.
Generally, it is specified as percentage of relay pick up current.
A relay plug setting (PS) have a value in the given range i.e. 50 to 200% .
Plug setting of 50% means as soon as current through relay coil increases above half (50%) of relay pick up current, it will start to operate.
Similarly, Plug setting of 200% means as soon as current through relay coil increases above two times (200%) the relay pick up current, it will start to operate.
If CT ratio is 300 / 5 A ,
then Relay pick up current (Ip) = 5 A
Thus,
If PS = 100% ,then Ip = 5 A corresponding secondary current = 300 A.
If PS = 50% ,then Ip = 2.5 A corresponding secondary current = 150 A.
If PS = 200% ,then Ip = 10 A corresponding secondary current = 600 A.
Is This Answer Correct ? | 0 Yes | 0 No |
How can i check a relay good or not?
why transformer rating is expressed in kva.
How to convert from HP to BHP please explain????????
Why DG self motor winding burnt out?
hi frnds.....anyone get any reply from HPCL. I HAVN'T.....B,COS written will b on FEB 17 th.
why should the lowest unit of a testing transformer ( cascaded transformer ) have higher power rating??
what is ACB and its function?
DIFFERANCE BETWEEN function of ELCB? function of rccb? function of mccb? function of acb? function of mcb?
how much current will take for 1kw power. and what is the eqoutiion which is connecting with kw and A.
why electric shock due to dc is dangerous than that of ac
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
0 Answers Eprosys Engineering Consultants,
What is OLTC in a transformer, specify its fuction.
35 Answers Bhel, Isgec, L&T,