there is one orifice plate already installed on 3" line, but
my previous engineer(who is not working here) removed that
tx, but now i want to take it in to the process, so now what
i have to do now? flow fluid is hytherm oil of temp. 260deg
& pressure is 3bar.
Answers were Sorted based on User's Feedback
In any industrial plant there will always be good records
and documentation on all equipment as well as all
instrumentation installed on the plant. The easiest in your
case is to find the FT tag number on the P&ID drawings or
the CCR faceplate and look at the data sheet of the missing
transmitter. The original calibration in differential
pressure will be on there as well as the model number of the
transmitter you need.
All you then have to do is calibrate the new DPT with the
diff press as per the data sheet and it will work as before.
In most cases the squire root extraction is done in the DCS
and not in the transmitter so try it just like this first.
The faceplate in the CCR will normally be set up to display
the min and max flow so that will not help you to find the
calibration diff pressure of the transmitter.
You can also try and find the original transmitter that was
removed and put power on it ans see what it was calibrated
for before. Even if the transmitter is faulty it might still
be able to display information. The is just as a last resort
since you cannot be sure if this calibration is what it
should be and it is better to double check it with the
documentation. This is just a method to double check
information.
As a desperate measure you can also measure the upstream and
downstream pressure as it is now during normal operation and
calibrate your transmitter to 1,5 that differential pressure.
For example:
Say your upstream pressure before the orifice is 300Kpa and
downstream it is 270Kpa you therefore have a DP over the
orifice of 30Kpa during normal operation.
Calibrate the transmitter for 0 to 45Kpa.
The flow indication inside the CCR will indicate the correct
flow since the extraction and the display is already setup
as it was originally. Have a look at what the % the flow is
indicated on the CCR faceplate. Since it is normal
operations it should be about 50% of the scale on the
faceplate. If it is not, modify the DPT calibration until
the current flow display about 50% of the full scale in the
CCR. You should be pretty close then.
This is not a very good or accurate way to do it and you
should keep on looking for the original design specs and
then re-calibrate the DPT when you found it.
Good luck
Is This Answer Correct ? | 5 Yes | 0 No |
Dear Nitin,
Ideally you shall have all the records, but in case if you do not have the records then try to recalculate the DP value using orifice sizing. You can get data for process condition from your process engineer and B (beta value / bore i.d. from orifice plate itself).
If you do not know how to calculate DP the please forward all the process condition with Line size, Line schedule and B beta value to anadkat.jigar@gmail.com. I can recalculate it for you.
Hope this will help you out.
Best Regards,
Jigar Anadkat
anadkat.jigar@gmail.com
Is This Answer Correct ? | 1 Yes | 0 No |
Close loop and open loop diagram for instrumentation
what is modbus & what signals are taken through it
What output voltage the proximity switch shows when it is in open enviornment?
Identify the electrical variable that is either directly or inferentially used by various instruments to determine the value of a measured variable.
why the output sugnal is 4-20 ma and not 4-25 ma?
What is the difference between dry contact and wet contact?
What is the difference between instrument earthing and normal earthing? and why is it necessary to do so?
What are different types of orifice plates?
what is Mv with respect to temprature in thermocouple
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
what is the responsibility of an instrument commissioning supervisor
what is the reset offset and control system in instrumentation