Answer / mrutyunjay mohanty
Dear Sir,
Greetings of the day !
Recently I have been through one answer shared by you and got your email id at AllInterview.com. Please kindly help me in my below concern :
Permissible current density equation i = (7.57*1000) / sqrt(resistivity * duration of earth fault)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mrutyunjay
Dear Sudhakar Sir,
Greetings of the day !
Recently I have been through one answer shared by you and got your email id at AllInterview.com. Please kindly help me in my below concern :
Permissible current density equation i = (7.57*1000) / sqrt(resistivity * duration of earth fault) as per IS 3043
Is this equation to be taken for all types of electrodes ( Plate, Rod or Pipe & Strip ) ?
Because , as per IS 3043, same equation is appropriate for plate electrode
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sudhakar.g
The earth resistance of single rod or pipe electrode is calculated as per IS 3040:
R=100xρ/2×3.14xL (loge(4xL/d))
Where:
ρ = Resistivity of soil (Ω meter),
L = Length of electrode (cm),
D = Diameter of electrode (cm)
Example:
Calculate number of CI earthing pipe of 100mm diameter, 3 meter length. System has fault current 50KA for 1 sec and soil resistivity is 72.44 Ω-Meters.
Current Density At The Surface of Earth Electrode (As per IS 3043):
• Max. allowable current density I = 7.57×1000/(√ρxt) A/m2
• Max. allowable current density = 7.57×1000/(√72.44X1) = 889.419 A/m2
• Surface area of one 100mm dia. 3 meter Pipe = 2 x 3.14 x r x L = 2 x 3.14 x 0.05 x3 = 0.942 m2
• Max. current dissipated by one Earthing Pipe = Current Density x Surface area of electrode
• Max. current dissipated by one earthing pipe = 889.419x 0.942 = 837.83 A say 838 Amps
• Number of earthing pipe required = Fault Current / Max.current dissipated by one earthing pipe.
• Number of earthing pipe required = 50000/838 = 59.66 Say 60 No’s.
• Total number of earthing pipe required = 60 No’s.
• Resistance of earthing pipe (isolated) R = 100xρ/2×3.14xLx(loge (4XL/d))
• Resistance of earthing pipe (isolated) R = 100×72.44 /2×3.14x300x(loge (4X300/10)) = 7.99 Ω/Pipe
• Overall resistance of 60 no of earthing pipe = 7.99/60 = 0.133 Ω.
If you have any doubt regarding this ...pls mail me sudhakar28485@gmail.com
Is This Answer Correct ? | 4 Yes | 5 No |
electical engg basic question
if i have to use 14 kw what size of power cable can i use and size of earth cable also.
why transformer measures in kva
Ceiling fan motor wiring Hi, I have 2 ceiling fans broken. The receiver/control units burned out due to lightening. One Harbor Breeze and one Hunter's I took them apart (remove receiver units). Now on both of the motor I see 4 wires coming out from each motor I really want to know the function of each wire. Are there anyway I can test to see which is which? After searching forums I know these 4 wires are from 2 sets of coils inside the motor, one is Start winding and the other is Runing winding I could not find the receiver/control unit any where, so I am planing to buy Capacitors and universal remote controls to make the fans run again. Anyone has any idea how to do the wiring, please help Thnks
why we do not get the electric shock at end of returning water of water cooled cable
A system absorbs 100 k J of heat and the increase in its internal energy is 100 kJ; the work done is
why they charge more bill for low power factor rather than high power factor
what is the meaning of osr in transformer.
How does a VOLTAGE OPERATED DIFFERENTIAL RELAY work??
What is trip and closing coil in cb? Why need of them
will we get shock from dc?
why a three phase induction motor cannot run at synchronous speed ?