This is about the recent problem that we have faced in our
project site.
We have 6/7.5 MVA. 66/11kV three phase star - star power
transformer. The neutral was solidly connected to the
earthing mat. But because of high resistance of earthing
mat (130 ohm on LV and 180 ohm on HV), one day LV side
neutral earthing conductor melted and we had a huge damage.

Can any one plz tell me what might happen when we connect
power transformer neutral to the earthing mat which has
high resistance (>100 ohm ) ?????

Answers were Sorted based on User's Feedback



This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/1..

Answer / k.prakashchandra

Have you measured IR properly, as the values are very high
?The IR should not exceed 2 ohms for a 66 KV MUSS .I do not
know whether primary neutral is to be earthed in case of
star/star tr.It is stated that LV side IR is 130 ohms ,and
hence the maximum earth fault current will be 50A.For 7.5
MVA tr the rated LV line current is about 400 A and EFR is
likely to be set at 80A.It appears that the earth wire
melted due to continuous earth fault current.If there is
conductor to ground fault at a distance of 100 m from tr
earthing ,there will be a pd of 63.5 V /m along the line
between the fault point and the neutral earth. If anybody
stands barefooted with feet 1 m apart along this line, he is
likely to be electrocuted as the power line does not
trip.Further the ground around the earthing also may be at
nearly phase voltage during earth fault

Is This Answer Correct ?    1 Yes 0 No

This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/1..

Answer / gairhe

I think you are right.

for the LV even if the imbalance neutral current is 10 A,
the 130 ohm resistance will produce GPR ( Ground Potential
Rise ) of 10 X 130 = 1.3 kV.

Also at the site the transformer neutral earth conductor was
touching the 185 sq mm single core copper power cable and
control cable. May be because of this high GPR , sparking
occurred and heat was generated.

The neutral earthing conductor is of size 95 sq mm. so 10 A
current is not a big issue.

In my view 1.3 kV and sparking developed heating at the
group of XLPE power cable, control cable and fire started .
Then the XLPE power cable was damaged and because of the hig
earth fault from the damage of XLPE cable, the near by
neutral earthing conductor got melted.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

A 400KVA Transformer has 400Hz frequency.if frequency is changed to 50Hz,then what will be the new KVA rating?

2 Answers   ABC,


What is the purpose of Vector Group in transformer?

1 Answers   Andritz, ThyssenKrupp,


features of hbc fuses

0 Answers  


How dc generators direction can be reversed ??

2 Answers   GPSC Gujarat Public Service Commission,


what are transmission line parameters and transmission line constants?

1 Answers  






difference between substation & grid substation?

2 Answers   GMR,


why we maintain 50hz ,220volts,20Amp,ratings fixed every where in india,,electricity

1 Answers  


DIFFERANCE BETWEEN function of ELCB? function of rccb? function of mccb? function of acb? function of mcb?

4 Answers   MacAir, Sajas,


what is the size of ht cable of 33kv ht line and transformers ratings are 1 Mva and 5mva.please send formula also.

0 Answers  


what is LT & HT?

6 Answers  


what is phase to phase to phase to ground fault

1 Answers  


i want to know about for what reason we are using star delta starter? how it works? what are the advantages?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)