This is about the recent problem that we have faced in our
project site.
We have 6/7.5 MVA. 66/11kV three phase star - star power
transformer. The neutral was solidly connected to the
earthing mat. But because of high resistance of earthing
mat (130 ohm on LV and 180 ohm on HV), one day LV side
neutral earthing conductor melted and we had a huge damage.
Can any one plz tell me what might happen when we connect
power transformer neutral to the earthing mat which has
high resistance (>100 ohm ) ?????
Answers were Sorted based on User's Feedback
Have you measured IR properly, as the values are very high
?The IR should not exceed 2 ohms for a 66 KV MUSS .I do not
know whether primary neutral is to be earthed in case of
star/star tr.It is stated that LV side IR is 130 ohms ,and
hence the maximum earth fault current will be 50A.For 7.5
MVA tr the rated LV line current is about 400 A and EFR is
likely to be set at 80A.It appears that the earth wire
melted due to continuous earth fault current.If there is
conductor to ground fault at a distance of 100 m from tr
earthing ,there will be a pd of 63.5 V /m along the line
between the fault point and the neutral earth. If anybody
stands barefooted with feet 1 m apart along this line, he is
likely to be electrocuted as the power line does not
trip.Further the ground around the earthing also may be at
nearly phase voltage during earth fault
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gairhe
I think you are right.
for the LV even if the imbalance neutral current is 10 A,
the 130 ohm resistance will produce GPR ( Ground Potential
Rise ) of 10 X 130 = 1.3 kV.
Also at the site the transformer neutral earth conductor was
touching the 185 sq mm single core copper power cable and
control cable. May be because of this high GPR , sparking
occurred and heat was generated.
The neutral earthing conductor is of size 95 sq mm. so 10 A
current is not a big issue.
In my view 1.3 kV and sparking developed heating at the
group of XLPE power cable, control cable and fire started .
Then the XLPE power cable was damaged and because of the hig
earth fault from the damage of XLPE cable, the near by
neutral earthing conductor got melted.
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the minimum winding resistance of 30hp compressor, to run or to switch on
which motor gives constant speed?
1 Ton = ? amperes & power. How much power 1.5 TON split AC consumes in an hour at 17 C , 26 C & 28 C (thermostat' temperature).
18 Answers Aamal, Ashiana Housing, Carrier, College School Exams Tests, Eastin Hotels, Godrej, LG, Medha, Medha Servo, Onida, Orean, PEL, Sahara, Voltas,
A 11 KV motor is working. if the supplay is fail. what will happened with it's breaker? Trip / remain the same condition?
If an induction motor is restarted before its rotor stop rotating, then what will be the amount of current drawn? Is this current will be the same as motor starting current?
what are the types of control systems to control the speed of the motor??
1hp= how much rpm
how to calculate cable size in transformer, distribution side?
what is the diffrence between R Y B phase and why it is called RYB
does buccholz in a transformer use batteries
difference b/w bus bar and tie line?if possible explain with eg:
sir i applied for hpcl(electrical).i want to know from which subjects most of the technical que will b asked.and pattern of the written test.pls help me
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)