A 11 KV motor is working. if the supplay is fail. what
will happened with it's breaker? Trip / remain the same
condition?
Answers were Sorted based on User's Feedback
Answer / nishad
The Motor will surely trip becaue by the sensing of under
voltage relay, it will give the trip command to the
breaker. once the breaker trip motor also trip. well in
cause of a small Voltage dip motor may not be trip. because
it's related to the setting of undervoltage relay.
somewhere it is set 2 second ( as per company's requirment)
if the power failure is more than set time of undervoltage
relay, motor trip
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
It will trip,if the breaker of motor has a voltage operated
hold coil which also provides protection against low voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / asish
the motor will not be tripped as there is no fault as only
supply is off.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / rajesh
as the supply power is constant, infinitely high current will flow through the circuit and hence the circuit breaker will trip.
| Is This Answer Correct ? | 0 Yes | 2 No |
why ac supply neutral should earth not in dc (-)
what is impedence of transformer? its formula
Why in Digital Megger for finding Insulation resistance,-ve is applied to core or conductor and +ve is applied to ground.
which type of starter is suitable for single phase motor ?
what is the vvvf in the dumbwaiter?? or lift. what is the actual process?/
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
will the introduction of capacitor bank parallel with the induction load reduce power consumption
4 Answers Nokia, WAPDA Water and Power Development Authority,
in three phase it represented by R-Y-B.what is full form of R-Y-B.
what is S.T?specify the range?
how to put cable sizing and cable glands size for respective cable & Cable Lug size in a DB sectors???
why should we connect the no load components in a equivalent circuit of transformer in parallel?why cant it be in series.
Its possible to use 3core 2R of 240 sq.mm cable for 3phases & separely 50sq.mm 3core cable fully for Neutral for connection of PCC to MCC 3ph..4wire system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)