Answer / rk
losses in transformer are 1) core loss2) copper loss
copper loss is proportional to current . the resistance of the copper changes with temperature. approximately it is 1.2 times at 85 degree celcius as compared to 40 degree ambient.so
total power consumed by the transformer during no load conditon can be read from the wattmeter connected in the primarry. this will give the core loss which varies with the loading of transformer insignificatly lets say 1000W.
now if transformer is distribution type or generation type.
maximum efficiency is when core loss = copper loss
so total loss at 50% loading is 2000w
copper loss at 100% load will be approx 4*1.2*1000=4800w( 4 due to doubling of current , copper resistance almost increases by 20% from 40 to 85 degree celsius rise
so total loss at 100% load = 1000+4800w=5800w
Is This Answer Correct ? | 0 Yes | 0 No |
.What is drip and drain.
why the steam turbine is not operated in home(base) load more than 1 hour kindly calrify
LAPT working in alternator / generator
I want to build 100 megawatt hydel dam. What does mean, 100 MW per hour? then how many electric bulb of 100 Watts the dam would lit?
our 125 kva DG does not start in AUTO mode works normally in MANUAL mode please give me a solution.....
How do you consider that you can improve and what assistance do you need to achieve this
what is need of primary water system in power plant?
what is the relation between the grid voltage and generator voltage how to link up generator with grid
why not maintain Ph 7.0 in Boiler because 7 Ph is not acidic and not basic.
2. what is meant by exhausthood temp?
what is voltage transformer explain in details
5 Answers Khulna Power, NCC, Reliance Power,
why drum level falls when one of the running coal elevations tripped?