how to calculate the watts from the tr
Answer / kesavan
if 1 TR = 12000 BTU
1 BTU = 0.29 w
so 1 TR = 12000 x 0.29 = 3480 w
approximately
1 TR = 3500 w (or) 3.5 kw
Is This Answer Correct ? | 7 Yes | 1 No |
For having nonavailablity of 10 Amps fuse, a lineman replace the same with 5Amps two strand, Do he correct ?
What is fuction of NGT/NGR using in Generator.
In our plant we have installed new MCC with ELR and CBCT which is detecting some leakage current in the system but it leading to some confusion when to check that in which feeder which is drawing current we put off the whole panel itself but still CBCT detecting some leakage current so can anybody ans me , where i am going wrong or how to detect whether its actual leakage or CBCT malfunctioning.
what is the effect of earth on capacitance in 3-phase and 1- phase transmission line?
What is Co-generation in the context of electrical power systems?
what is meant by VFD ?where its useful ?
Why do we perform an open-circuit test and short-circuit test on the transformer?
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
I find that underground strip-armoiured,4core,LT PVC cables in an earthed power distribution sytem are occasionly found in charred condition-with no trace of it except ash. Is this because of no proper earth connection/continuity (giving rising to high armour resistance)in the joint enroute or because of insufficient capability (again due to high armour resistance)of cable-armour to carry fault current or due to neglected /unprotected overloading of the cable or due to high armour currents caused by power thefts where only phase(s) are unauthorisely tapped & at the point of poer consumption earth terminal is established by burring underground a not so good earthing rod (or using an underground water pipe for the purpose)
it is possible to run 130V AC and 230 V AC cables run in same tray
what is the difference between relay and a contactor.
What aturn on methods of scr?