In control valve , Failure position : Close
If it is Fail close(FC) during failure of AIR.. what will be the initial/ normal position of control valve is it normally open or close? please some one explain soon..
Answers were Sorted based on User's Feedback
Answer / bhargav purohit
Hi,
I think your question has it self an answer. Your valve is Air fail to close. Means if there is no Control Air/signal, your valve will be closed .
In running plant condition, Position of valve could be anything according to process.( Fail to open or close depends on process requirement)
Suppose you want maintain a Tank level and safe condition is full tank, then..
1> if you are maintaining level by inlet water flow to tank, your valve should be Fail to open. Means in case of signal failure your valve will open and fill the tank (Safe condition)
2>If you are maintaining level by output flow, then you should select fail to close vale. So in case of failure of control signal, output flow will be closed and tank will be full.
Regards,
Bhargav Purohit
Is This Answer Correct ? | 12 Yes | 0 No |
Explain about 4 wire instrument concept & tell about its wiring fron sensor in Field to PLC panel.Explain with an example?
Name some of the common protocol use in automation.
What means zero and span in transmitter callibration.
what is zero trim and span trim?. at which problem we need to use this?
I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea
what is seebeck effect?
what is input and output cards of plc needs to be hot swappable mean
Ohm’s law, kirchoff’s law, pascal’s law, Bernoulli’s therem,
I want to apply for the universities in US,but i got the GRE score of (650+300=950)TOEFL 69/120.Is this score sufficient for applying universities please i am married i need to go to US because my husband didn't get H1 yet.please send me suggestion
What is input and output of vaiberation transmitter and what is its unit.
how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?
modbus and profibus communication difference?