How to carry out hot loop checking of closed loop pf
temperature control valve & temperature transmitter?
Answers were Sorted based on User's Feedback
It can be done by following the steps below.
1. Take the control loop in manual mode.
2. Block the temperature control valve position manually to
the desired value.
3. Now check the loop as per the normal loop checking
procedure i.e. feed 4-20ma and observe the output value on
the DCS.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / senthil.doosan@yahoo.com
simple..
there is no hot loop check or cold loop check..
as u mentioned u have a temp transmitter and control valve
so,u have 2-AI and 1-AO
-connect the simulator by removing the DCS cable of the temp
transmitter,then give 4 - 20 mA and check with DCS reading
-give 0 to 100% command from the DCS for AO to operate the
control valve.then check the feedback in the DCS(AI)
conclusion,ur loop is ok...
| Is This Answer Correct ? | 6 Yes | 2 No |
in mass flow meter what is drive friquancy ?
In dcs panel we are using diff type of modules ?what is module ? what is the use of modules ?diff type of module?
Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,
in the boiler in the main steam line and its bypass line and the startup vent vales are only motorised valves why cant we use other types of valves such as pneumatic.
who discoverd ohms law?
how many maximum enter 2mm Dia solid cylindrical pipe into 8mm Dia hollow cylindrical pipe. give answer with calculation.
what is the input of ph sensor and meter during the calibration time and what is the output?
How many input(Analog and digital) and outputs(Analog and digital) are there in DELTA v DCS Version 7.0?
Why we use mmwc unit for pressure
LADDER LOGIC Can any body state Logic on following condition Instructions to use 1-XIC 2-XIO 3-Output ONLY Program Push 1st button On - 1st lamp should On Then Push 1st button Off - 1st Lamp Should remain on Push 2nd button On - 1st lamp should Off and 2nd lamp should On Then Push 2nd button Off - 2nd Lamp Should remain on.
what is ZERO SUPPRESION and ZERO ELEVATION?
how to calibrate Necleuonic level transmitter.?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)