If the load is 10Kw and power factor has to improve from 0.5
to 0.8,how can we select the capacitor rating
accordingly.Illustrate by showing formula?

Answers were Sorted based on User's Feedback



If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / guest

at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)

Is This Answer Correct ?    10 Yes 2 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / prasad damodar bhoir

kvar= kw (tan phi 1- tan phi 2)
cos phi 1= 0.5, phi 1= cos inverse 0.5= 60
cos phi 2= 0.8, phi 2= cos inverse 0.8= 36.86
kvar= 10 (tan60 - tan 36.86)= 10 (1.73-0.74)
kvar= 9.9

Is This Answer Correct ?    4 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / h salim

Load = 10 kW
cos phi 1 = 0.5
cos phi 2 = 0.8

Rating of capacitor Qc = kW(tan phi 1- tan phi 2 )

Is This Answer Correct ?    3 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / prakash g.r.

Calculation of Required Kvar

Initial or Present Power Factor =Qi,
Required Power Factor = Qd

KVAr= KW(TANQi-TANQd)

Qi=COS-1PFi = Initial Power Factor Angle

Qd=COS-1PFd = Final Power Factor Angle

Is This Answer Correct ?    3 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / ahatesham

at 0.5pf Apparent power is 10/0.5=20VA
reactive power = 17.321kVAR.
At 0.8pf
APPARENT POWER =10/0.8=12.5VA
Reactive power=7.5kVAR
So we need to provide (17.321-7.5)=9.821kVAR reactive power
through capacitor to bring of up 0.8 from 0.5.
So we need a capacitor rated for approximately 10kVAR to
achieve the target.
ANS= CAPACITOR RATING 9.821kVAR (approximately 10 kVAR)

Is This Answer Correct ?    2 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / nagesh.patwari

Kvar = KW * [ tan (cos^-1* Current PF) - tan (cos^-1* Required PF)]

Is This Answer Correct ?    0 Yes 0 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / lohith

kvar=kva*sin

Is This Answer Correct ?    2 Yes 3 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / rk

How did you Calculate Apparent Power=20VA to Reactive power 17.321 KVAR simlarly 12.5VA to 7.5KVAR As the formula is KVAR=KVA/KW

Is This Answer Correct ?    0 Yes 2 No

If the load is 10Kw and power factor has to improve from 0.5 to 0.8,how can we select the capacitor..

Answer / nag

unity powerfactor

Is This Answer Correct ?    0 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

ganaretors A check B check and C check details

1 Answers  


what is the formulae for calculating the cable size for a given voltage and current.

4 Answers   Bharat Forge,


What is the name of powder which is used in inner side of a cable? and purpose?

1 Answers  


how calculate gd2 of ht motors

4 Answers   Hindustan Copper Limited, Kohler India,


What is the general power factor & min. power rating of TV,LCD type TV, CRt type TV, Scanner, printer?

0 Answers  






whatis mean by voltage?

7 Answers  


can alternators work at leading power factor?

2 Answers  


In LRS how much water PH value maintain for good operation of motor?

3 Answers  


how will be power factor while using the resistive load and Capacitive load?

3 Answers  


can we use ELCB and RCBO in one db

6 Answers  


why in india the voltage generate multiply by 11,,,like 220v,440v,11kv,33kv,66kv,220kv,

3 Answers   NTPC, Servotech, Tata Power,


what is the transiant condition in alternator? and how it can be prevanted?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)