i want use pressure transmitter for flow ,how?
Answers were Sorted based on User's Feedback
Answer / vishnu
It is not possible to measure flow using pressure transmitter.We need DP transmitter to measure flow.First we have to create a DP using ventury tube or a orifice plate.the flow rate is directly proportion to the squreroot of the Diffrential pressure.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / mokie
use differential pressure transmitter with oriface, vcone or
the other means
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / sudarsun
Differential Pressure transducer along with a Venturi pipe
should do the work. The pressure at the normal diameter vs
the pressure at the shorter diameter should be proportional
to the rate at which the fluid flows.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ahmed
You can't use the pressure transmitter to measure the flow
because when you want to measure the flow you need delta be
in the pressure and the presser transmitter have one side
you want transmitter with high and low sides
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / jobby c johnson
In any Flow meters(venturi, Oriface etc), Flow rate is given by the expression
Q is propotional to sqrt(delta p)
Where Q is mass flow rate ; delta p is the differantial pressure across the transmitter
| Is This Answer Correct ? | 4 Yes | 1 No |
What is the diffirence between Earth and Neutral and What is the required normal voltage between earth and neutral
Q1]IF THE RANGE FOR FLOW IS -35 TO 125 WHAT WILL BE THE SPAN FOR ABSOLUTE AND FOR NORMAL? Q2]HOW TO CALIBRATE CAPILLARY TYPE LT? Q3]HOW MANY ERROR CALCULATIONS ARE THERE USED IN PROCESS INDUSTRIES? Q4]HOW TO CALIBRATE TEMPERATURE TRANSMITTER? Q5] HOW TO CALIBRATE LEVEL TROLL AND HOW TO CONNECT? Q6]PLEASE TELL ME THE BASIC FOR INSTRUMENTATION WHICH IS APPLIED FOR CALIBRATION AND FOR ALL? PLEASE MAIL THE ANSWER TO honest_yes@yahoo.in
How to check electrical health of Vibration probe?
May I have a brief note above the voltage barriers? Whats is the purpose? Please mail me if you've operational details, mail id: rajkumar.diice@gmail.com
why are set -10vdc in bently neveda vibration system.
How to convert gpm into inches of eater.I nerd formula with example so pls help me.
What information needs for Control Valve "sizing"
find the kp ki kd from the transper function G(S)=29.44s+04707/1.5349s2+s
What is the working principle of Bentley Nevada 3300
What is the load line in control valve?
What is ptw and write 3 types of ptw?
how to do loop checking pls email to shanavaska2000@yahoo.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)