why the transformer neutral earthing is to be done by copper
flat only,if we use GI flat what is the disadvantage.
Answers were Sorted based on User's Feedback
Answer / pradyumna chandra panda
Earth electrod should have low resistance and copper flate meet it. IF we use GI flate then potentional between earth &neutral will be increase on unbalance load, but it is allowed only 20 volt . we can decreare the earh resistance by increance the electrode in parallel.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / balu
Copper flat is low resistance than
compared to gi and it has good
mechanical strenth.
Is This Answer Correct ? | 1 Yes | 1 No |
i have done my b.tech in 2009 .still hunting for a job...wat shud i answer if intervevwr asks..(what u have done 1yr)
What is broken wire condition in transmission line?
what is transformer
63 Answers ABB, Advance Power Controls, CERC, Electrical, Electrical Supervisor Competency Certificate, ETA, IBM, Jindal,
am commissioning the trafo without connecting the neutral therefore unbalance will occur what is the alternative solution for this?
When color of silica gel will gets change from blue to pink from Top to bottom?
What is the criteria for deciding whther fire wall is required between two power transformers
Why we are going for converter transformers for DC drives application instead of distribution transformer?
Alternators are invariably star connected why?
how to control the generator output voltage? what r the condition should satisfy for synchronization?
WHY DG are rated in KVA or MVA ???., but ALL power plants are rated in KW or MW.,,?
how much air gap in induction motor as per the Indian standards?
what is the diff. b/w restricted earth fault relay & standby earthfault relay and where they are used?