IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN
WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED,
SO WE CAN SAY THE PROBLEM IS IN
Answer / carl_ellis
The problem is in the controller's PID tuning, which is
tuned to be too sluggish.
All of the loop's control components work properly:
- the transmitter reports the process variable
- the controller responds to an error (albeit too sluggishly)
- the control valve responds to the controller's output, as
evidenced by switching to manual mode
The PV response as reported by the transmitter depends on
the controller's appropriate response to error. If the
controller's response to error is sluggish, then the loop's
PV response will be sluggish.
Manual mode offers a means of overriding the PID's
calculated output value and driving the output to where it
needs to be.
This question qualifies as one of the best interview
questions I've read on this site. I'll be sure to use
this question when I interview candidates.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
why 4ma show higher zero ? i have transmiter flow renge 0-1000 m3/h but 4 ma show in monitoring 200 m3/h and 20 ma show 1000 m3/h i want when 4ma show 0 m3/h and 20ma 1000m3/h
What are the processes Variables?
what is the difference between 3,4 wire RTD sensor?
6 Answers HTA Instrumentation,
What is differnece between leveltroll and interface leveltrol?
please explain about actuator action? direct action & return action ?
I have applied the post Junior Engineer-(TM)in R.R.B CHANDIGARH recently . what type of question i have to practice and which book ?. can i get any model question paper?
centrifugal compressor interlock? Tell me the parameter at which compressor will trip
diffrence b/w accuracy and precision?
If the Barrier Fails during online then What will be the control valve position in field or Positioner action in the field.
Q- voltage source of 12v is driving the circuit.if circut draw the current of 0.5A them source voltage will became 11.8v.what is the power dilevered by source when circuit draw 5A current ?
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)