a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of
0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy
of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag
What is the accuracy ratio? is this ratio acceptable?
Answer / markwilcon
Transmitter=0.005 x 2500 = 12.5
comparison gauge = 0.001 x 3000 = 3
Am i on the right track?
| Is This Answer Correct ? | 1 Yes | 0 No |
WHAT ARE THE INSTRUMENTAL DIAGRAMSOF VALVES?
0 Answers Artikal, ITC Infotech,
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
What is the difference between DCS and SCADA?
What is sensitivity of K type thermocouple? Is polarity important in thermocouple connections?
What is the cascade control system and where is use in power plant give the detail with block diagram
What is the solution if rotork motorised control valve showing pink Colour in dcs.
3 Answers Bhushan Power Steel,
Waht is surge in compressors and how to control it?
Difference b/w SCADA & DCS
How can we cheak the ENCODER ?
1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling
what is the input to be given digital temp controller during the the calibration time?
Can we use PLC in Hazardous Area?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)