why 4ma show higher zero ?
i have transmiter flow renge 0-1000 m3/h but 4 ma show in
monitoring 200 m3/h and 20 ma show 1000 m3/h i want when 4ma
show 0 m3/h and 20ma 1000m3/h
Answers were Sorted based on User's Feedback
Answer / automatic
put an offset to avoid the values nears Zero
I mean around 3.99 ma & 4.01 ma, you can do this from a
software, or from coditioning block, or you just shift you
zero to a signifiant flow to rcord.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / dinesh priyadarshi
1) Set LRV & URV by HART
2) set zero at your desire value by HART
Is This Answer Correct ? | 0 Yes | 0 No |
why can't we use 5-20mA standard or some other instead of 4- 20mA?
Hi..i am B.E. (elect.&comm.)..i m workini in a bio mass power plant as inst. Engg. I want 2 know about growth in big power plant sector..is this field is good 4 me ..i m electronics engg..? Plz plz reply..
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
How to convert mmWc(mili meter water colam) to tph(ton per hour)?
A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic meter/hr. Thorough impulse line flushing and zero calibration has been done, yet problem persists. What do you think is the problem and how do you rectify this fault?
can anyone tell me about the basic concepts to consider before to start a PLC panel wiring
How many mode are in ups?
how can calibrate vacume trasmitter by HART COMMUNICATOR ?
what is reset windup in integral control?
how to calibrate 0- 150 psi presure gauge by dead weght tester
why is honed type flow orifice plate? what purpose it used? how to select this?
For what reason would you possibly be compelled to make use of a Smith Predictor. Explain the idea behind the operation of this device.