in 11kv/400v transformer when only one phase of 11kv supply
fails what happens to sec voltage and why
Answers were Sorted based on User's Feedback
Answer / sunit
from my point of view what i have seen physically .. if one phase of the 11kv line is faulty or jumper in transmission lines burnt out then there will be a low voltage in the secondary side of transformer,
actually DTR breaker in control room needs to trip the circuit but if the relay time settings are not accurate then it won't trip the circuit rather show low voltage in the secondary side...
Is This Answer Correct ? | 2 Yes | 0 No |
If delta/star ,one phase voltage will be normal and the
other two 50%, If star/star two phases normal and the third
missing
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / b.janardhana rao
I seen physically. One phase of 3 phases failure in HT. I said Example it will shows like RY - 415, YB-415, BR - 230Volts in seconary side. In that time two phases what loads are there is working. Remaining phase is not working. So 3 phase loads like pums, motors are not working. So we can put in ACB phase failure relay to be used. In that case the ACB breaker wads tripped.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / suresh
HT side one phase fails means secondary side unbalance voltages coming ,that means upstream side breaker will trip within time limit.
Is This Answer Correct ? | 0 Yes | 2 No |
11kv/415v T/F is designed for 3 phese supply , if 1 phase
fails then t/f will trip automaticly and no voltage will be
avaliavle at secondary side.
Is This Answer Correct ? | 11 Yes | 17 No |
Answer / m.prasath
Here,
Primary voltage is 11kv.
Secondary voltage is 400v.
If primary voltage is failed means nothing will happen in secondary side. ie almost zero in secondary side in transformer....
Is This Answer Correct ? | 6 Yes | 12 No |
why we use ac?why we use dc? why we we cannot use only ac/dc for all the applications?what happen if we use?
why we are using in reverse power relay in generator singranizing
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
Percentage losses in power generation?
What is the purpose of shunt trip in ACB function?
i m doing DEEE in part time,can i join regular cources in BE,,IF i join what the cources can i select like (civil,ece,IT) ,,kindly advice
What is the tension required for the 25000 CFM AHU belt
why humming sound occured in h HT transmission line
if flux and load static in dc motor and supply voltage increases 20% then what happened in speed
what is the min and max dc voltage for a dc system (110vdc)
if we convert kw into Ampers,which one formula use by us,pls tell me?
what is the difference between Power and Distribution transformers ?