if a dp transmitter has range 100 in H2O and flow is 20mmcf
and if the flow is changed to 25 mmcf then what is the
formula to determine new range of transmitter
Answer / carl_ellis
design max flow rate = 20 mmcf
design max DP = 100 in H2O
new max flow rate = 25 mmcf
new max flow rate = ?
The max flow rate increases by 125% over the design max flow
rate:
25/20 = 125% increase
DP calculations are done in normalized percentages. 125% = 1.25
To calculate the corresponding DP at a max flow rate 125%
higher than the original, where X = DP
sq rt of X = 1.25 (square root of normalized percentage
of DP)
X = 1.25^2 = 1.562
1.562 = 156.2% (work in normalized percentage)
156.2% of 100 inH2O = 156.2 in H2O at a max flow rate of 25 mmcf
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
WHAT IS DIFFERANCE BETWEEN INSTRUMENT AND EQUIPMENT
what is Least Value of MICROMETER?
How can we check Zero of DP type Level Transmitter onside?
What materials are used in thermo wells?
in my plant 100% feedwater control v/v is air to close but due to instrument air fail,the valve opens but instead of drum level high its get tripped in low low drum level.the urv of level tx is 0 and lrv is -800.pls tell me the reason. for such behaviour.
what is axial shift n what is differential expansion in turbine? how many sensor probes r mounted for this n how it works?
why ultra sonic level transmitter is installed in 90 degree?
Why the industry's standard current standards are from 4mA to 20mA,not from 0mA or any other range?
What is cut off relay? And why use in PLC and DCS?
Identify and use the ANSI/ISA-S5.1 consensus industrial standard process symbols.
Why do we have earthing cable in branch cable and shield in the same cable?
0 Answers Process Control Technologies,
what is difference b/w the solinoid volve and autodrain?