how is a displacer type level transmitter calibrated.explain the method?
Answers were Sorted based on User's Feedback
Answer / a.moin
A displacer type level is most commonly level application
used for the closed vessel as well as interface level where
the two process liquid having diffrent specific gravity.
Its works on the arthmedics principle or the loaw of
buoncy, the law say the weight of the substance immerse in
the liquid is equal to the amount of liquid displaced by
the body.
Now as per the question the way to calibrate the displacer
level first we have to isolate the level troll chenber from
its process by isolating the root valves,
then drain the liquid presence inthe chamber, connect the
PVC transparent tube at the bottom of the cahmber and then
start filling the water in the tube.
For zeroing
fill up the water into chember and adjust the zero check
this function two or three times....
compensate the S. G of diff liquids Prcoess S.G= 0.7 and
water S.G= 1.0
to calibrate the transmitter for span 0.7/1.0 *100= 70%
fill the water upto 70% adjust the span
For dry calibration of displacer you should knwo these
details below
Displcer weight: 2400 grms (2.4Kg)
volume of Displacer: 1620.84 by ^r2h..
displacer diameter: 7.620 centimeter
length of displacer: 35.56 centimeter
Note: the limitation of displacer cannot be exceed more
than 72 inches....
Is This Answer Correct ? | 20 Yes | 4 No |
Answer / haridass kwt
To calibrate the displacer type LTs by fixed in the w/bench,
First remove the head, clean displacer and chamber and
assemble,
fix the calibration setup (drain isolation, clear tube and
marked scale),
Calculate 100% position of fluid filling, by the Sp.
gravity of the fluid where the LT being used. (Ex: If sp.gr
is 0.8, then the 80% of the displacer height to be marked
in chamber due to the water used for calibration), and mark
every 25% in chamber ouside for reference.
Fill the water and check the transmitter/board/sensor
response approximately.
Fill the water till the displacer touches. and chk 0% and
adjust to 4mA.
Fill the water till 100% to check span and adjust 20mA.
(If the LT s not responding, replace LVDT/board and chk)
Repeat zero and span check 4-5 times and the chk every 25 %
rising and falling.
If ok, the prepare the calibration report and tag it.
Is This Answer Correct ? | 11 Yes | 1 No |
What is SLPC & MLPC? How it works?
If fire would be inside the plant which fire detector is to detected the fire.
how to tune the closed pid loop?
Any can guide for QA/QC Inspector in oil & gas region, the procedures, formats standards, design criteria, i search in all enginees but i can't found wat i need?????????
4 Answers Aramco, Asian Paints,
WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??
In a gas over oil actuator, after the opening/closing of valve, how the gas is vented out? How does the hydraulic/gas circuit function?
Can DP transmitter with orifice plate works on Beta ratio 0f 0.3 and differential pressure of 100 MMWC in liquid service application?
we callculat main steam flow by D.P. but where is H.P. & L.P. IN Orfics?
what is the zero elevation and zero supresstion in level measurement, how can use it?
When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?
hey any one got the papers of SAIL and HPCL plz do help me by posting them to my mail ID's naren07_87@yaho.co.in, surenarendra@gmail.com
what is mass flow meter, working principle of mass flow meter and its installation.