how is a displacer type level transmitter calibrated.explain the method?
Answers were Sorted based on User's Feedback
Answer / a.moin
A displacer type level is most commonly level application
used for the closed vessel as well as interface level where
the two process liquid having diffrent specific gravity.
Its works on the arthmedics principle or the loaw of
buoncy, the law say the weight of the substance immerse in
the liquid is equal to the amount of liquid displaced by
the body.
Now as per the question the way to calibrate the displacer
level first we have to isolate the level troll chenber from
its process by isolating the root valves,
then drain the liquid presence inthe chamber, connect the
PVC transparent tube at the bottom of the cahmber and then
start filling the water in the tube.
For zeroing
fill up the water into chember and adjust the zero check
this function two or three times....
compensate the S. G of diff liquids Prcoess S.G= 0.7 and
water S.G= 1.0
to calibrate the transmitter for span 0.7/1.0 *100= 70%
fill the water upto 70% adjust the span
For dry calibration of displacer you should knwo these
details below
Displcer weight: 2400 grms (2.4Kg)
volume of Displacer: 1620.84 by ^r2h..
displacer diameter: 7.620 centimeter
length of displacer: 35.56 centimeter
Note: the limitation of displacer cannot be exceed more
than 72 inches....
| Is This Answer Correct ? | 20 Yes | 4 No |
Answer / haridass kwt
To calibrate the displacer type LTs by fixed in the w/bench,
First remove the head, clean displacer and chamber and
assemble,
fix the calibration setup (drain isolation, clear tube and
marked scale),
Calculate 100% position of fluid filling, by the Sp.
gravity of the fluid where the LT being used. (Ex: If sp.gr
is 0.8, then the 80% of the displacer height to be marked
in chamber due to the water used for calibration), and mark
every 25% in chamber ouside for reference.
Fill the water and check the transmitter/board/sensor
response approximately.
Fill the water till the displacer touches. and chk 0% and
adjust to 4mA.
Fill the water till 100% to check span and adjust 20mA.
(If the LT s not responding, replace LVDT/board and chk)
Repeat zero and span check 4-5 times and the chk every 25 %
rising and falling.
If ok, the prepare the calibration report and tag it.
| Is This Answer Correct ? | 11 Yes | 1 No |
why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?
What is the use of gauge?
IN CONTROL VALVE SPECIFICATIONS GENERALLY TERM " DE- 200" ."DM -400"USED,, WHAT IS DE/ DM STANDS FOR?
how manys ways dp transmitter can be calibrated having range of -150 to 400mmwc,what side pressure u will apply?
What is the difference between HMI,SCADA and MMI,not abbrevation?
How do you calibration D.P transmitter? ?
where proximity sensor installed on tank in loading arm application
why would you like to join our company
what are the different types of Protocols? & their applications.
6 Answers Infosys, Sitara Chemical Industries, Syntel, VSNL,
what barrier is used in process industry.
3 Answers ADMA OPCO, Process Industries,
can someone tell me about electronic speed switch &how it conect with proximittyswitch?(with dgm)
give some question relative instrument fitter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)