Will it be OK to connect a 5MVA 33/6.6kV Ynd11 Transformer
to a Star connected Motor. Or on other words connecting a
Delta to a Star.
I have another 30MVA 33/11 Dyn11 and would it be practical
to convert it to Dd0 consequently converting the Voltage
Ratio to 33/6.35kV Dd0.
yes. what is the capacity of motor?
In your case , grid voltage is 33kv, Yn connected.Hence
power transformer has neutral connection brought
out.Neutral CT is installed to detect the ground faults.
secondary of 5MVA tranformer is 6.6kv,
This is Feeder bus voltage.6.6kv Feeder bus feeds Motor (
star connected). and Feeder bus is not interconnected to
another source. It is independent.This 6.6kv rotates at 30
lagging to primary3kv system.
Motor must be use inverse & instantaneous time
overcurrent and earth fault ( CDG61+cdg12) or equivalent
manufacturer protection
we use delt to star as weelas star 6.6motor.
No problems experienced.
In the othercase to change a 30MVA,33/6.35KV IS
REDESIGN/MANUFATURING. iT IS EXPENSIVE.No use at all and
advantage. You should change 6.6kv sw.gr also.
Is This Answer Correct ? | 1 Yes | 0 No |
what is magnetizing current test in power transformer
Write the difference between OCB,VCB ?
what are pilot cells
What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?
What is the relation of current with torque when motor started in Y-connection???
why onlyseries motors are used as universal motors? why not shunt?
one cable insulation resistance 200 mega ohm. how find 250 meter cable resistance.
What is the approximate percentage of Si content in transformer core(CRGO-Cold Rolled Grain Oriented)? Why it is kept so low?
What is the difference between Welding Transformer and Normal Transformer?.
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
if voltage is not builed up in small generator what will be the reason?