I want to know what must the CT ratio be on a load of 300A
is a 3PH nutral to earh installation?
Answers were Sorted based on User's Feedback
Load current is 300A. The equipment shall withstand the
starting current -which is around -5-8xIn.It is preferable
to select 1ooo-1200A/1A OR 5A.
WE ADOPT THIS THUMB RULE for our protection setting& co-
ordination.
Is This Answer Correct ? | 0 Yes | 0 No |
The neutral is a point in power transformer or in motor
connection where all phases are connected.In this point
voltage is zero. when you connect thisoint to earth, the
fault current or capacitance circulating current flows to
earth.
when a fault occurs , current is high.Therefore,CT ratio
should be 1000-1200/5 or 1A.
It is usually upto designer or protection device supplier.
Is This Answer Correct ? | 0 Yes | 1 No |
about transformer oil material & Test name for the measurement of its dielectric strength & wht will u do if its dielectric strength goes low ?
what is the installation process for lifts
what is load flow?
DEAR ALL I have motors ( 10 units )each one is 90kw 380V 50 HZ 1000rpm but new local pwer is 220v 60 hz requierd rpm should be 1000 pleas what the beast solution is used frequncy converter or rewinding all motos or chang all motors thanks
Is it possible to import & export power through the same power transformer? what will be the vector group normally for both different or same?
what is the difference between electrical & electronics?
what is phase angle ? and also tells me why my phase-phase voltages are 390 rather then my single phase voltages are 221 and 223 respectivly?
What is the direction of rotation of blades in a table fan and in a ceiling fan ?
How to calculate the transmission losses incase of overhead transmission lines?
how fluoresent lamp works??
why we use 50hz frequency in india why not other frequencies like 52,59,42 etc
What are the reasons for AVR failure in LT DGsets ?