Can I Drain A Oil For Sample When The Transformer is
Running? (Charged)
Answers were Sorted based on User's Feedback
Answer / ranjan ghosh
Yes you can,but there is some matter you think first,
1)The total volume of tranformer oil,i.e when u r taking
oil sample it should not effect transformer total oil volume
(i.e it should negligeble effect)
2)you should take care of your safety first.
3)after taking oil sample oil sample valve should tight
properly.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / k.prakashchandra
Yes but you will have to take bottom sample only considering
safety.This sample will give average test results as the oil
is circulating.For correct results ,you have to test bottom
and top samples separately after cutting off supply.
Is This Answer Correct ? | 2 Yes | 0 No |
how the CT and PT is connected in the circuit during testing of transformer explain with diagram
what is slip ring startor
Min and max capacities of VCB,ACB,ACCB,OCB,MCCB and MCB
What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???
How to calculate fault level of 11 KV system
What Should be the value of Vector Surge angle at Tripping and how to calculate it?
what is the role of energy meter in distribution system ???? technical and non technical losses in distribution system????
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
Why the Voltage rises when Leading Power Factor is occurs?
how much insulation resistance 11kv & 33kv under ground cable between earth to phase & phase to phase.
Which type of arc protection devices used.
hi friends can u tell me name of the sites where i can get animation of electrical machines......