What are methods to avoid the inrush current at the time of
starting of power transformer ?

Answers were Sorted based on User's Feedback



What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / suresh kumar

We cannot avoid inrush current when any transformer is
switched on after a long period of shutdown. Only thing we
can do is minimising it by charging the transformer by the
lowest voltage (using tapp changers)and we can avoid
spurious tripping by inrush current by using only
transformer differential relays in which an inrush current
filter is used.

Is This Answer Correct ?    15 Yes 1 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / vinothbabu.k

BRFORE STARTING ON THE TRANSFORMER WE SHOULD SWITH OFF ALL
THE OUTGOING FEEDER FROM THE DISTRIBUTED PANEL BOARD,THEN
ON THE TRANSFORMER WITHOUT CONNECTING ANY LOAD, THEN SWITH
ON THE FEEDER ONE BY ONE,R CONNECTED LOAD.THIS THE METHOD
TO AVOID THE INRUSH CURRENT FROM THE TRANSFORMER...

Is This Answer Correct ?    13 Yes 4 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / mukhesh

their is no chanses to avoid the magnetic inrush currents
in p t/f by wn inrush curens come the t/f will doing the
vibrations to avoid vibrations steel chains are fixced

Is This Answer Correct ?    0 Yes 0 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / makku

we can reduse inrush currrent by using winding having high reactance

Is This Answer Correct ?    0 Yes 0 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / priyan

You can reduce the second harmonic by using the DELTA
connection in the CT’s but I prefer to play with the
protection relay parameters, in this case it is better to
control the differential current, there is 2 slopes for the
differential zones, try to increase the slope N01 to get
passing the inrush current.
By filtering the 2 nd harmonics, refer to relay co
ordination and set the values

Is This Answer Correct ?    1 Yes 2 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / vijay

apply a coil before applicable circuit

Is This Answer Correct ?    3 Yes 7 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / karthikeyan

Its recommended to install an CLR (Current Limiting Reactor)
befroe the Power Transformer to reduce the inrush current.

Is This Answer Correct ?    3 Yes 7 No

What are methods to avoid the inrush current at the time of starting of power transformer ?..

Answer / a.kossay

TO AVOID INRUSH CURRENT IN TRANSFORMER WE MUST USE A
VOLTAGE SENSE RELAY TO MONITOR THE VOLTAGE PEAK , SO WHEN
ITS VOLTAGE PEAK THE C.B CAN BE CLOSED AND INRUSH CURRENT
WILL BE LIMITED

Is This Answer Correct ?    1 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

How to back charge the Gas turbine generator

0 Answers  


please send the IS strandard for electrical to sakthi_murugan86@yahoo.co.in

0 Answers  


Could u pls tell me the NPCIL electrical engineering interview questions for Executive trainee, and also guide me how to face the interview.

0 Answers  


What is creepage distance..... what will be the value for different voltage level

0 Answers  


Describe the colour rendering properties of i) tungsten filament lamps ii) tubular fluorescent lamp

0 Answers  






usually why bettery voltage are 1.5V, even if you open a 9V battery there are six 1.5V batteries in series. is it not possible to increase this voltage other than putting in series

1 Answers  


12.5 KVAR capacitor 440V gas filled, Its used for windmill purpose, How can i know about microfarad value for this capacitor

2 Answers  


what is distribution board?

0 Answers  


For a 6.6kV Motor it is recommended to do megger test with 500 V d.c and not more than 5kV d.c but the Hi voltage withstand test should be performed by 12kV AC. Why the dc voltage test should be limited but AC voltage withstand test could be with such a high voltage?

0 Answers   Hormozgan Steel,


clarify types of motor operated valves and advantages

0 Answers  


transformer is connected with 50hz and 60hz at same rating which will give more output on same rating

2 Answers   Palace Consultant,


Active power= VI COS FI But incase of leading power factor ( more than unity), may we use other formula ? because the cos fi (value of cos thita) should not be grater than one.

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)