If any control valve create hunting problem, what is the
possible reason and solution?
Answers were Sorted based on User's Feedback
Answer / imran
check as
1-put the controll valv in manual and check incoming signal
if stable then problem in controll valve
2- check positioner condition its feedback link ,incase of
smart poistener check feedback potentiometer.spring and
configration.
3-check diaphragam
4-gland packing
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / bhavesh
check the gland packing,check the positioner o/p is
unstable,check the small leakage on actuator.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / muhammad arsalan afzal
1=First of all check the feedback link of positioner mostly
such type of problem occur due to feedback link looseness.
2=Gain of the controller is too high you have to adjust it.
3=Gland packing is too tight slightly lose the gland pusher's
screws.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / s.k.bakshi
1. First check the positioner air supply and the positioner.
2. If problem persists tune the PID.
| Is This Answer Correct ? | 8 Yes | 7 No |
Answer / suman chakraborty
check I/P signal means I/P and O/P whether the AFR o/p of I/P is stable or not.and check the AI Chanel of I/P.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dhaval joshi
First check actuator position..removed power from the
actuator...and accordingly connect first power supply
cable,after connect command and feedback cable.
| Is This Answer Correct ? | 1 Yes | 6 No |
what is modbus & what signals are taken through it
If i have 4 Allen Bradely make RS logix 5000 PLC and for viewing that we are using 4 RS view SCADA for 4 different packages. Now, I will want to view two packages on only one SCADA. Then how i will do it?
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
what is dry leg and wet leg in transmeter calibration?
How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
Which Signal hart communicator work? If there any signal change when hart connect while transmitter in line ?
how we convert Mili ampere to temp txt,level txt,flow txt,pressure txt range value
How works weighfeeders in cement industry? what is the working principle?
what is mean by hot loop and cold loop testing, whts different between both
pl give the guidance for DUBAL written test
what are the diff. in servo and regulatory control?
What is actuator what is motorized control valve?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)