How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
Answers were Sorted based on User's Feedback
Answer / noori
Hi
there are two methodes of temp.tx calibration:
1 - if u have MV sourse u have to get ambiante temp.MV & the
temp. you select and using themocouple vr. MV chart to get
the corresponding MV for these two temps.and for the same
thermocouple type
you have to subtracte the MV for ambiant from the MV for
your temp.
then yiu can inject this new MV to the input of the Tx
you have to get two tempretures for the calibration one for
ZERO &the second for span
you have to do the above prcedure for both points
2 - if you have temperature calibrator the you have to use
the same type of thermocouple immering it directly in the
calibrator and set the first point for Zero & set the second
point for span adjustment
| Is This Answer Correct ? | 3 Yes | 1 No |
IF U USE MV INJECTOR FOR THERMOCOUPLE CALIBRATION.........
FIRST U SHOULD MEASURE THE ROOM TEMPERATURE AND TO COMPUTE EQUELENT THERMOCOUPLE VOLTAGE.......V REF....
IF U R INJECTING 100 DEG EQULENT MV U SHOUD DEDECT V REF MV FROM THAT ACTUL MV...AND APPLY ADJUST 100.......
IF U R USING TEMPERATURE CALIBRATOR NO NEED THIS ONE ...U CAN APPLY DIRECT......BECAUSE IT GIVES THE COMBENSATED OUTPUT
| Is This Answer Correct ? | 3 Yes | 3 No |
My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
In which principles tx ,pressure gauge,Temp gauge,control valve works?
0 Answers Bajaj, Professional Instruments,
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
Boiler flame scanner advantage?
0 Answers Fluke, Petrochemicals, Tata Chemicals,
What is full form of hart communicator?
what is the formula for calculating milliampere at different pressure points for eg 4-20 ma = 3-15 psi but if i have to check the ma at 4.6 ma?
If fire would be inside the plant which fire detector is to detected the fire.
how to calibrate pressure gauge(we can not able to fixed by pointer screw adjustment and pointer re fixing method)
what is the principle of vibration
What is a snubber circuit?
why 4 to 20 ma ,why not 0 to 20 or 3 to 15 or anything
19 Answers Honeywell, TCS, TN,
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)