what is o2 analyzer and how it measured ,what is the role of
this analyzer in cfbc boiler...
Answers were Sorted based on User's Feedback
O2 analyzer is used in all types of boilers like CFBC and
AFBC etc..role of this analyzers to measure the O2
concentration after the ECONOMIZER ,it is a normal value like
(3 to 4) no problem ,if any variotions obeserved based on
that value we can increase/decrease SA fan air into the boiler
| Is This Answer Correct ? | 20 Yes | 1 No |
Answer / msp
:- If analyzer showing wrong on DCS than first I will
forced the analyzer value on the DCS if any tripping taken
from it.
Through the Multimeter checked the value 4 to 20 mA on DCS
or same on field As per define range in the DCS as well as
analyzer transmitter. If all things are correct than its
calibration was got disturbed. For the calibration
1 For the calibration we need sample gas and instrument air.
2 Connect the both input instrument air and sample air
through the rotameter for flow control of the both air and
sample gas.
3 Power on the analyzer and communicate hart communicator
with the analyzer.
4 For the zero calibration apply the sample gas with the
help of rotameter for flow control on the analyzer. And
press enter on the zero calibration on the hart
communicator.
5 For the span calibration apply the Instrument air with
the help of rotameter for flow control on the analyzer. And
press enter on the span calibration on the hart
communicator.
After calibration save the setting with the help of the
hart communicator.
And cross checked the same 4 to 20 mA by given the
instrument air and sample gas accordingly.
| Is This Answer Correct ? | 11 Yes | 0 No |
how to use K thermocouple instead E- type without compesation cable
what is function of PLC, and how is it work , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
typical loop drawing of a simple feedback control comprising of one transmitter and one control
What is the difference between modbus,fieldbus & profibus
Question on maha cement
How can corrosion alter the accuracy and precision of a C- Bourdon tube pressure gauge?
NSV type probe stands for
suggest a sensor to measure rapidly varying temperature?
.how does CSADA systems display the process variable value?
What are the different modes of a contollogix family processor? How they work?
where the use of direct action control valve?
why the derivative in PID is always set to zero?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)