Answer / carl_ellis
Any thermocouple measuement requires 2 temperature measurements
- hot junction measurement
- cold junction measurement
A cold junction is created at the point where
non-compensation wire is connected to the thermocouple wire.
A measurement without compensation wire AND without a
corresponding cold junction measurement is not valid.
The only way to take a K type thermocouple measurement (or
any type thermocouple measurement) without compensating
cable is to use a temperature transmitter configured for the
type of thermocouple because the transmitter will perform
the cold junction measurement at its wiring terminals.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 0 No |
In case of Transmitter's(e.g.Ultrasonic Flow meter ) we have an normal practise of selction of upstream and downstream distance such as (20D and 5D ).can anyone please let me know whow to calculate "D" ?? i guess it refers to pipe thickness is t right ?
Steve said that "An eddy-current probe works by passing an alternating current through a coil of wire and measuring the coil’s impedance" while we are using -24 Volt DC , So I am confused about DC and AC. Plz .
2 Answers Jindal, Sadara Chemicals,
HOW WE MEASURE A DRUM LEVEL BY DP TRANSMITTER ? WHAT IS ITS FORMULA ?
Can we use twisted pair cable instead of ethernet for communication?
warning lamp does not light, but it does light when the wire from the lamp going to the sending unit is grounded (the part that plugs into the sending unit) what does this indicate)?
how can calibrate vacume trasmitter by HART COMMUNICATOR ?
Please anyone answer my question, what is the difference between single acting and double acting control valve, in what condition we better choose single acting rather than double acting
What do you know about gail?
how can be calibrate flow indication transmitter (rosemount) it shows excess milli amps nearly about 24 ma on full scale, but its scale was set on 20ma on full scale..???how can be simiulate..???
Can any body tell me about SAP MAINTINANCE MODULE. WHAT IS its function and application. And study material Source about it. I shall be very thankful.
how to calculate temp.prapotional to mv in thermocoulpe.
Difference between ultra sonic flow meter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)