If the maximum demand is 120 KVA in a building, then what is
the Current taken according to load given ? Formula for it ?
Answers were Sorted based on User's Feedback
Answer / jose
120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr
| Is This Answer Correct ? | 6 Yes | 0 No |
a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120
| Is This Answer Correct ? | 2 Yes | 1 No |
Why electric traction is used ??
what is the capacity of storing mass electricity.
what is the responsibilities of electrical project engineer?
what is the use of compensation in designing a transmission line
What is current divider rule (cdr)?
if earthing is used in place of neutral how the circuit completd.
Inverter. converter. Ups.MCB.solar.alternators. motors.
Why iron core transformers not used in high frequency applications ?
What is installed in PAC that is control the humidity
10rm cable can got load ---- amp? Or Which Size Cable can take the load 100amp capacity SCR; breaker.
1 Answers B-Con Trade Associates,
What type of a DC motor would you use for a lift?
what is DAR test?
2 Answers Al-Naboodah, ISRO, ONGC,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)