If the maximum demand is 120 KVA in a building, then what is
the Current taken according to load given ? Formula for it ?
Answers were Sorted based on User's Feedback
Answer / jose
120 kva means you have to supply 3 phase load.
3 phase load with 415 v and unity pf can take a current
according to eqn kva=1.732*Kv*I
I=120*1000/(415*1)=290 A appr
Is This Answer Correct ? | 6 Yes | 0 No |
a Generator of 1KVA can supply upto 1.4 amps, so the maximum load could be 1.4*120
Is This Answer Correct ? | 2 Yes | 1 No |
What is the difference between LT CT & HT CT?Can we use indoor type transformer as an outdoor type or vice versa?
What are the basic & Majour problems in UPS ?
0 Answers Roto Power, RotoPower,
In the diesel generator if there is an AVR (auto voltage regulator) gone faulty, in this condition is there any way to generate the voltage from the alternator? I need a brief explanation can you please help somebody
why a three phase induction motor cannot run at synchronous speed ?
what is power factor? is it good or bad for a system? what will happen if power factor increase or decrease?
why there is no current in the rotor body althrough the flux linking with it also get changes. why current only flows in windinds not in rotor
what is the difference between RMS meter and normal meter
If I have a motor of 1MW with 6.6kv, running at 35% load, how can i save energy without reducing the load ?
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
what is the use of Turbocharger in a gen-set?
how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?
hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"