I have a 1000 kVA Transformer(11kV/0.415kV) and a APFC panel
of 400 kVAR(LT).Now if i want to remove the LT APFC panel
and install a HT(11kV) APFC panel on the HT side is the HT
APFC panel will work same as the LT APFC panel(improve the
power factor),if yes what will be rating of the HT APFC
panel?what is the formula to calculate HT APFC panel rating???
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The power on HT side is equal to power on LT side +
3%(1.6%). The power rating of APFC remains the same.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / kathiravan
Since the PF is corrected "before" the bank is connected
(EX:A--------B---------------C----------------D-----------E.
Suppose If the bank is connected the location @"C",the PF will be corrected from location A to C only,where as location C to E will not be effected by the installation of location C)there wont be much effected weather to locate capacitor either primary or secondary of the transformer.Rating of the capacitor must be the respect of HV/LV supply voltage.
Is This Answer Correct ? | 1 Yes | 1 No |
(1) From the following option, which option is correct for largest size transformer.? a)1KVA,25Hz , b)1KVA,50HZ , c)1KVA,60Hz , d)1KVA,100Hz
EXPLAIN WORKING PRINCIPLE OF ALTERNATOR & MOTORS.
what is differant beetween overload current and phase current?
why protection meter is always connect to star
PLEASE INFORM ABOUT THE IDEAL TEST RESULTS OF MAGNETIC BALANCE TEST OF TRANSFORMER 33/11 kv DELTA-STAR T/F
WHAT IS THE DIFFERENT BETWEEN MCB & MPCB? & HOW IS USE?
why do we lay up the core of a cable?
how to test the electrical panel.ht lt mcc pcc.
advantages of vvvf drives over non vvvf drives for EOT cranes
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
Is there any Electrical supervisor license which gives permit to work whole India rather than individual state??