What is the winding resistsnce need to be in a 1000kva,
11kv/415v transformer, between ht winding to lt winding, ht
winding to earth, lt winding to earth.?
Answer / k.prakashchandra
You mean insulation resistance ?As a rough guide,the megger
value should be at least 2 M ohm per KV rating at 60'C for
11 KV and above.The megger value doubles itself for every
10'C fall in temp.
Is This Answer Correct ? | 1 Yes | 0 No |
How to check the Bushings of the transformer?
How can we step up ac and dc ?
How to select, design,size & calculate for 11 KV/33KV/66KV/132KV/220 KV/440 KV circuit breaker for HT side of transformer protection/HT distribution protection?
what happens when you connect a.c and d.c supplies
what is the meaning of ceiling voltage in Generator exciter?
Due to velocity saturation, MOSFET reaches saturation a.Before Pinch off b. After pinch off c. At Q point d. Before Q point e. After Q point
Purpose of providing neutral isolation panel for parallel operation of diesel generator
Please explain the following and how these are working with PLC unit 1.I/O Module 2.I/O Device 3.Adaptor Card 4.Ribbon Adaptor 5.RS 485-FC
0 Answers Shree Mayur Engineering,
why make protection 85% of winding?
what happen if we give square wave instead of sine wave to the transformer
How Calculat the Cable Sizing of HT/LT System & Explian by one Exampal?
Alternators are invariably star connected why?