Answer / nagaseshareddy.m
significance of per unit impedance is reducing the
complexity of calculation. Zp.u=actual
impedance/baseimpedance
| Is This Answer Correct ? | 20 Yes | 1 No |
Answer / praveen
In power system values of impedence will be large so to
reduce its complexcity in calculation it is expressed in
per unit....
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / mafika
p.u impedance represents the amount of volt drop that's
going to occur in the transformer and also helps in the
fault calculations
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / tiwari
P.u calculation is done to
simplify the calculation per
unit impedence is
convenient in case of
transformer because both
primary and secondary p.u
impedence is same
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ravindra
it's dimentinalless quantity not having any units, it can
be converted refer to primary or secondary.
| Is This Answer Correct ? | 7 Yes | 7 No |
Answer / parviz
By per unit impedance, we are able to deal with R, L and C in the same way as a resistor.
| Is This Answer Correct ? | 0 Yes | 0 No |
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
Where double earthing is required? Is there any power specification to have double earthing?
Difference between field rheostat and armature rheostat.
what is cogging and crawling
Where is servomechanism used?
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
How can I calculate the require lumen of a room. If I use Tube Light (40 W), Or 100 W incandescent lamp. Please give detail answer.
how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
In Plug used in house,Why Earth of the plug more thicker & deeper?
Whata are the types of Cables?
What is a soft start?
How can I calculate ISF of current transformer?
0 Answers Cigniti Technologies,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)