Profibus DP is a multi-master system. Would it work on RS-485
4W or not, and justify your answer
Answer / carl_ellis
The Profibus DP specification defines the hardware transport
physical layer as 2 wire RS-485. The communications
protocol and the transport layer are both part of the
Profibus DP specification (the separate 2 wire cable for
24Vdc power supply is not involved with the communications).
Any device that passes Profibus DP certification will
conform to the Profibus DP specification.
Therefore, a 4 wire RS-485 device will not work on a
Profibus DP network because it won't be a Profibus DP
device, it does not meet the Profibus DP spec, which is 2
wire RS-485.
Attempting to operate a 4 wire RS-485 device on a Profibus
DP network will only disrupt Profibus DP communications on
the network.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 1 No |
how can I install "operating system " in may HART communicator? It is damaged, and it doesn't boot up.
Where is wet leg is used?
Explain ratio control system.
Hi..i am B.E. (elect.&comm.)..i m workini in a bio mass power plant as inst. Engg. I want 2 know about growth in big power plant sector..is this field is good 4 me ..i m electronics engg..? Plz plz reply..
1. what is 3 point calibration & 5 point calibration? 2. If we use hart communicator to set the LRV & URV of a smart transmitter, did we calibrate the transmitter? why? 3. Make a complet list if meterials needed to properly connect a pressure gauge to a steam pipe using 1/2 inch stainless steel tubing. The gauge connections is 1/2 inch NPT-M and the steam pipe tap has a 1/2 inch female coupling, compression fittings are use. 4. What are the tools in loop checking? 5. What would the ISA symbol of a square root extractor look like? 6. What would you do to completely prepare for the configuration? 7. What safety measures must you undertake when doing configuration? 8. what are the two most commonly use programming languages used when we configure a PLC? 9. What would you do if you accidentally skipped a step in the configuration procedure? 10. How would you know if the configuration were sucessful? 11. Name at least 3 selections available when we configure the burnout protection of a controller?
3 Answers EI Electrotechnical Institute,
When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?
I HAVE PRESSURE TRANSMITTER WITH TWO WIRES 24 VOLTS SUPPLY.IF TRANSMITTER WILL GIVE SIGNAL TO THE DCS WHAT HAPPEN TO THE 24 VOLTS POWER SUPPLY IT WILL DROP OR REMAIN TO 24 VOLTS POWER SUPPLY.
what is the calibration standard for pressure and differential pressure transmitters?
DEAR SIR/MADAM MY NAME IS ARKAPROVA BHATTACHARYYA.I AM A FRESHER INSTRUMENTATION ENGINEER.CAN YOU PLEASE SEND SOME QUESTION PAPERS OF GRADUATE ENGINEER TRAINEE EXAM OF DVC(DAMODAR VALLY CORPORATION).MY EMAIL IDs ARE arka_aec@rediffmail.com.
i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i engergize the transmitter the meter shows 0 or 100% no variation in it.the distance of two points is 19.5 inches, i am in trouble please suggest me what can i do it's very urgent Please reply me as soon as possible Best regards ikraam haider
defination of radial vibration?
SOME OF YOUR QUESTIONS ARE NOT MAKING ANY SENSE SO TRY AND PUT IN A LITTLE BIT MORE EFFORT BEFORE YOU POST A QUESTION. WE WILL ONLY HELP THOSE WHO WE CAN SEE ARE TRYING TO HELP THEMSELVES.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)