I HAVE PRESSURE TRANSMITTER WITH TWO WIRES 24 VOLTS SUPPLY.IF
TRANSMITTER WILL GIVE SIGNAL TO THE DCS WHAT HAPPEN TO THE 24
VOLTS POWER SUPPLY IT WILL DROP OR REMAIN TO 24 VOLTS POWER
SUPPLY.
Answers were Sorted based on User's Feedback
Answer / carl_ellis
The measured voltage across a regulated power supply will
remain at 24Vdc. If the voltage across the power supply
drops below 24Vdc, then either the power supply is too small
to carry the combined load or it is faulty.
The measured voltage across the transmitter will vary
according to the loop current.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / carl_ellis
You describe a situation with a 24Vdc power supply, a 250
ohm dropping resistor and a 2 wire loop powered transmitter
at 4.0mA
To get the voltage to vary across the transmitter, you have
to change whatever the transmitter is measuring to get its
output to change, or force an output with a HART
communicator. The loop current does not vary on its own,
it varies in response to whatever the transmitter is
measuring.
Carl's Loop Rules
The voltage across the power supply remains constant: 24Vdc
The voltage drops across the transmitter and analog input
vary with the current in the loop.
Assuming a bench setup with very short wire runs and a very
low wire resistance, then if the analog input dropping
resistor is 250 ohms, then
at 4.0mA the transmitter drops 23.0V, the AI resistor drops
1.0V
at 12.0mA the transmitter drops 21.0V, the AI resistor
drops 3.0V
at 20.0mA the transmitter drops 19.0V, the AI resistor
drops 5.0V
The sum of the voltage drops must equal the power supply
voltage.
You can bank on it.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
how can I install "operating system " in may HART communicator? It is damaged, and it doesn't boot up.
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
1.Give example of analog and digital signal 2. What is yhe advantage of 8086 than 8085
5 Answers Bhel, College School Exams Tests, Profitec,
What is profibus?
Which boiler is use in power plant
how pressure transmitter work, what is its principal to measure and how its generate signal. for pressure transmitterinstallation which precautions must be taken ??
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
how to derive kg/cm2 to mmwc? complete derivation.
whats the reason for control valve not installed -90degree (down position)
What are the types of control valves available
in mass flow meter what is drive friquancy ?
Can we use thermocouple in generator of power station replace RTD(pt 100)? if we don't have any place for use RTD.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)