3 ph motor connected in star delta starter. when we start
the motor it run in star but when in is going in delta it
trips the main incoming supply. why?
Answers were Sorted based on User's Feedback
Answer / deepak r thakur
simple when motor start in star three phase going to
winding correctly but when its going in delta motor two
winding connect with 440votl but 3rd winding connect same
phase so motor going in singal phasing & its get heavy
currunt it trips the main incoming supply.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rajesh kumar sharma
Two conterctor hold on star running time after some time a conteractor whose shrt three terminals has unhold and delta conteractor is hold it change only one sccond time.
if the timer switch is not working than creat a problam.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / anurag tiwari
Dear friend,
there are three point u have to check
1)first u check the motor winding.
2)check the timer and set the delta time.(appox 6sec).
3)If u are using mpd relay .May be your CBCT is saturated.
| Is This Answer Correct ? | 0 Yes | 0 No |
wich type of cable is selected for wiring of 20hp motor?
where they are using surge arrester and lighting arrester? how they connect? what is the purpose of that?
what is the question paper model for section engineer in RRB
IF avr is voltage regulator of genset means why we are giving genset CT sense to AVR ?
what is the difference between the characteristics of two different phase bushing of any transformer
When the DG is running at the time we can connect to capacitor banK? why it is required or not
Squirrel cage induction motor has constant A slip B stator current C rotor resistance D speed at all load
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
wts d diff b/w C.T. & P.T.?
If carbon brushes spring tension either loose or tight, what happen on Motor performance During Full load Operation?
why do we prefer alternating current in india where as in USA prefers DC?
If the t/f capacity is 500KvA then what is Amps ratting of the main breaker.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)