If the t/f capacity is 500KvA then what is Amps ratting of
the main breaker.
Answers were Sorted based on User's Feedback
Answer / athar abid
As we Know that
KVA = Sqrt 3 . Voltage(V) . Current(I)
Now for 400V (Phase-Phase) syayem
I = 500KVA/(1.732 * 400)
=500*1000/(1.732*400)
=721.7 Amps
There is no standard breaker available with this rating, so
take one step above rating i.e. 800Amps
Hope its clear.
Regards
Athar Abid
| Is This Answer Correct ? | 1 Yes | 1 No |
The unit of resistivity is:(a) ohms(b) ohm millimetre(c) ohm metre(d) ohm/metre
What is the LUX
HOW CALCULATE MOTOR KW, IF MOTOR NAME PLATE MISSING, WE FIND ONLY MOTOR WINDING RESISTANCE ONLY
In CTs tan delta point should be earthed , what is the reason behind it?
wat is syncronization . wat parameter will take for syncronization.
what happen when ac motor is connected with dc current
What is the real use of reactive power in a electrical system other than loss (inductive &capacitive).I want to know its real physical significance.
what is the value of combined earthing in general electrical circiut?
0 Answers Cathtect Engineering,
What are the different protection systems used to protect the transformer internally and externally?
what is the difference between id fans and fd fans
12 Answers Perkins Thermal Systems,
Why short ckt does not happen when solenoid coil connected to supply. as its a wire only.
Why in power plant projects we see DOL starting method used for motors upto 160 kW instead of star delta method
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)