we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why
not we convert directly from 66kv to440v?
Answers were Sorted based on User's Feedback
Answer / shariff
It can be step down from 66kV to 440V,but the problem is
above 33kV power transformers will be in treated as EHV,
and normally they will carry loads in terms 20 or 12.5MVA
etc. then for e.g for 20MVA the sec. current with 440V will
be 20x10E6/440=45kA( Normal rating), where this power
transformer cant be made practically with huge cuurent. So
practically we will go for 66kV to 11kV normally, where
Current is the limiting factor...
Is This Answer Correct ? | 32 Yes | 4 No |
Answer / k.prakashchandra
Inside a factory it is feasible.But for public utility you
can not erect regular 66KV/433V substations say ,every 500
meters, as long LT distribution lines can not drawn in view
of current and voltage drop.
Is This Answer Correct ? | 11 Yes | 3 No |
It increases the power transmission cost very high.
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / jaheerabbas
if we are converting the 33Kv to 440v directly, wastage of
power is more in the form of heat,so that we required large
no of heat sink too....heat sink cost will be more compare
to transformer, so that we go for the step by step convertion
Is This Answer Correct ? | 14 Yes | 10 No |
Answer / lakesh thakur
when we convert 66kv to 440v directly then transformer size
will increase & loses will also increase. So we should
increase the size of heat sinke. So directly we can say the
cost of whole our project will increase & also increase MVA
rating
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ved prakash
Basic insulation level at HV & LV side is also a big factor.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ramki
fulls , there is mutual coupling in between the windings , so for 66/33/11/133..like this we can found the mutual coupling as a nearly 1.......so wethis
Is This Answer Correct ? | 2 Yes | 11 No |
Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?
We all have seen transmission and Distribution lines In transmission lines the voltage is high and current is low(to reduce I^2r loss) and in distribution lines voltage is low but current is high however the size of transmission wires is bigger than that of distribution wires even though the amount of current carried by the distribution lines is more than that of transmission lines why?
Can Dy11 and Dy1 vector group transformers be paralleled?
where the protection CT in neutral of transformer be located, before bifurcation or after bifurcation and why.
why transformer rating in kva?
How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.
Hello Guys !! i want to rrb section engineer electrical(signal) previous model papers? any body help me?
What is an ideal transformer?
what will be the min and max voltage flow from neutral to earth?
whats the advantage and disadvantage in TUMETIC mdel transformer
Who are the manufactures those manufacturing 3Cx2.5sqmm FRLS cables. I heard about FRLS technology adopted only in wires useful for wirings
what is the difference between OD and VL