Dear sir/mam
Iwant complete details of Naintenence of 33kv/433v
Transformer having 1250 KVa
Dear friend,
In routing maintenance you should take care of the
following .
Daily .
1. Percentage loading of a transfomer
2. Make sure the bucholze realy is full with oil no inert
gas is there if there then purge the same.
3. Check the record the Reading of OT & WT
4. Check manualy for any leakage from any part of the
transformer.
5. Check for any abnormal heating & noice in transformer.
Quarterly.
1. Check & change the silica gel of the breather .
2. Check teh Safety function tripping of HT breaker related
to transformer. ( tripping point of OT , WT & Tranfomer )
Annualy.
1. Check & fillter the Trasformer oil
2. with complete shut down take the reading of insulation
resistance of the transformer winding.
3. Open & check the condition of transformer HT & LT
bushing for any cracks or damage.
4. Chceck the condition of the earthing pit & take the
earthing resistance value for all the earthing pit (
Neutral & Body earth )
Do the same as directed & have a trouble free operation of
the transformer for a long period of time
Is This Answer Correct ? | 3 Yes | 0 No |
A 11 KV motor is working. if the supplay is fail. what will happened with it's breaker? Trip / remain the same condition?
What is the meaning of key single line diagram?
what are the available sizes of pin type terminal lugs in the market today?
For backup batteries connection,which method is best? series or parallel ?
I want to know how to calculate the size of electricity cable in building?
0 Answers DR Engineering Services,
need of capacitor used in plant
what is the formula to calculate voltage drop/loss on 66KV Transmission Line?
why generator and t/f ratings given in kva?
What is water cooled chiller plant?
how to calculate the distance relay faulty zone?pls explain?
WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SIZES??
14 Answers Dubai Group, Saudi Delta Groups, Savitha Electricals,
list the advantages of RCCB over other circuit breakers?