Answer / tarun aggarwal ymca
what u have to first take into mind what type of cable u want to purchase....then its size matter
usually we use XLPE insulated cable for Power cable and Aluminum or copper its depend upon the cost and loses
mean if u need large length cable you have to prefer aluminum in shorter length copper cable is preferred as its resistivity is less
for example
VLL = 11kV (line volatge)
L = 1.3km
Maximum allowable Vdrop = 2.5% of VLL i.e.Vdrop = 275V
SkVA = 3000kVA (Total Power we have to transfer of to be used by the connected load)
Full load Current If= SkVA/root3 VLL i.e If = 157.5A
Demand factor is what we actually demand the current (it not always full load current what we demand) Let D.F = 80% of If
Id =D.F x If (Demand Current) where D.F = Demand Factor i.e Id = 126.0A
The cable current carrying capacity is always kept larger than the demand current let S.F for Cable in % = 30% Extra Id
Ic= (1+S.F/100) Id i.e Ic = 163.8A
This current is what will be safer current that will be carried out by cable
Now derating factor K is calculated by the following equation
K = Kground x Ktherm.res x Kdepth x Kgroup
Vdrop = 3IdL root(Rac cos􀄳+ Xsin􀄳)
Now cable data is refered
Type 3 Core, Copper Conductor, XLPE insulated, Copper tape Screened, PVC bedded, Steel Wire Armoured, PVC, 8750/15000V.
Parameter -------- 50 mm2---- 70 mm2 ------ 95 mm2------- 120 mm2 ------- 150 mm2 ----- 185 mm2
Irated (A) --------- 187----------- 227- ------------ 267--------------303 -----------------338------------------ 383
Kground----------------0.86
Ktherm.res-- ----------- 1
Kdepth-------------------0.98
Kgroup ------------------0.7
K-------------------------- 0.590
Icor (A) -----------110.32 --------- 133.92----------157.52--------- 178.76-------------199.41------------225…
Rac (ohm/km) --- 0.493 --------0.342------------ 0.247------------0.196---------------0.1… ------------ 0.128
X (ohm/km) --------0.118 --------0.112 ------------0.106------------0.102------…
P.F = Cos--------0.85
(In radian)-------- 0.5548------ 0.5548----------0.5548-----------0.5548-…
Vdrop (V)-----------196.76-------167.73-------…
Considering the values of Ic, Icorrected and Vdrop the best suited cable is 120 mm2
cable for connecting switchyard to substation
Sorry extra long answer but i want to explain in detail
| Is This Answer Correct ? | 7 Yes | 2 No |
what is a kit kat fuse?
what is MEMS and any one of it applications?
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.
0 Answers Bhushan Power Steel,
what is transistors comprised of?
What is the calculating formula for HT and LT amps in a transformer.
Why corona takes place?
how can found motors folt current ? how can disided circuit breakers caoicity and breaking capicity ?
What is the basic difference among Circuit breaker,Contractor and Isolator? Are they different names of same device/equipment?
The maximum demand of consumer is 2 kW and his daily energy consumption is 20 units. Its Load Factor is (1) 10.15% (2) 41.6 % (3) 50 % (4) 60%
How To increase Knowledge Of boliler regarding To Only Electrical Field..
in parallel operation of power transformer why the distance between power transformer and capacitor bank feeder is necessary to know
tell me about your project
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)