What is the formula to find out cross sectional area of
cable for certain current rating?
Answer / tarun aggarwal ymca
what u have to first take into mind what type of cable u want to purchase....then its size matter
usually we use XLPE insulated cable for Power cable and Aluminum or copper its depend upon the cost and loses
mean if u need large length cable you have to prefer aluminum in shorter length copper cable is preferred as its resistivity is less
for example
VLL = 11kV (line volatge)
L = 1.3km
Maximum allowable Vdrop = 2.5% of VLL i.e.Vdrop = 275V
SkVA = 3000kVA (Total Power we have to transfer of to be used by the connected load)
Full load Current If= SkVA/root3 VLL i.e If = 157.5A
Demand factor is what we actually demand the current (it not always full load current what we demand) Let D.F = 80% of If
Id =D.F x If (Demand Current) where D.F = Demand Factor i.e Id = 126.0A
The cable current carrying capacity is always kept larger than the demand current let S.F for Cable in % = 30% Extra Id
Ic= (1+S.F/100) Id i.e Ic = 163.8A
This current is what will be safer current that will be carried out by cable
Now derating factor K is calculated by the following equation
K = Kground x Ktherm.res x Kdepth x Kgroup
Vdrop = 3IdL root(Rac cos􀄳+ Xsin􀄳)
Now cable data is refered
Type 3 Core, Copper Conductor, XLPE insulated, Copper tape Screened, PVC bedded, Steel Wire Armoured, PVC, 8750/15000V.
Parameter -------- 50 mm2---- 70 mm2 ------ 95 mm2------- 120 mm2 ------- 150 mm2 ----- 185 mm2
Irated (A) --------- 187----------- 227- ------------ 267--------------303 -----------------338------------------ 383
Kground----------------0.86
Ktherm.res-- ----------- 1
Kdepth-------------------0.98
Kgroup ------------------0.7
K-------------------------- 0.590
Icor (A) -----------110.32 --------- 133.92----------157.52--------- 178.76-------------199.41------------225…
Rac (ohm/km) --- 0.493 --------0.342------------ 0.247------------0.196---------------0.1… ------------ 0.128
X (ohm/km) --------0.118 --------0.112 ------------0.106------------0.102------…
P.F = Cos--------0.85
(In radian)-------- 0.5548------ 0.5548----------0.5548-----------0.5548-…
Vdrop (V)-----------196.76-------167.73-------…
Considering the values of Ic, Icorrected and Vdrop the best suited cable is 120 mm2
cable for connecting switchyard to substation
Sorry extra long answer but i want to explain in detail
Is This Answer Correct ? | 7 Yes | 2 No |
what is the difference SCR & TRIAC?
Why 66KV is step down to 11KV and then 433v, not directly 66KV to 433v ?
3 pahase 750kva Running 2 DG sets in 35 mints.525ampers. and 616 kw how much fuel consumption in Generator.what is the formula.
1 Answers Delite Systems Engineering,
What are dependent sources?
what is the exact meaning of power
what are the accessories need to be added while doing estimation for the following: 1.MCCB 2.MCB 3.ACB
For a stable system, where should the poles of a system be in a root loci plot?
what parameters are should nessary for control technic dc drive(in rolling mills)?
What is the rating of HT SUBSTATION and LT SUBSTATION?
Explain working of PIU(Power Interface Unit) in Telecommunication,
7 Answers ACME, ATC, Bharti, HCL, INDUS, Pace Pharmaceuticals,
Whag is the PS class of accuracy of CT?
What are the advantages of hydropower?