The maximum demand of consumer is 2 kW and his daily energy
consumption is 20 units. Its Load Factor is
(1) 10.15% (2) 41.6 % (3) 50 % (4) 60%
Answers were Sorted based on User's Feedback
Answer / rishi kumawat
Load factor = avg.load /(maximum load on given time period)
Load factor =(20/2×24)= 41.6%
Is This Answer Correct ? | 59 Yes | 5 No |
Load factor = av load / peak load 20/24 kw is the av load .
Ans is (2)
Is This Answer Correct ? | 20 Yes | 17 No |
Explain difference between aluminium coductor & copper coductor.
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
What is metering cubical? What is the use?
Plz tell me how we can find that particular company has vacancy or not
ynchronous M/C with under excitation with reactive power absorption , acts as a) synch. Motor b) synch gen c) synchr capacit
Post possible questions for Power Factor Panel FAT / SAT
how we can calculate cable size of 230v,1 hp single phase motor ? panel to motor distance is 25 meter
the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?
How power is transferred from one winding to another in an auto-transformer? A) electrically B) magnetically C( both a & b D) neither of above
In our domestic single phase line if you don't have a ground connection (earthing)how will you separately use earth in a specific power supply board.
harmonics filter
what is tan delta measurement?..... why that terminal is earthed.....?