Dear all,
Can anybody tell me that how to choose CT for a specific
load? I have a 200kw induction motor, which ratio CT should
be installed? Is there a formula or calculation that
determines the CT ratio for a load?
Regards.
Answers were Sorted based on User's Feedback
Answer / guest
I dont know of any formula to answer your question, but I
follow a trial method which worked out well for ME.First
know your full load current and the expected running
amperes which would be below your full load amperes.Now
choose your ampere meter which will show your running /full
load amperes at about 75% of the chosen amp meter scale.Now
you can select your CT .
In this case a 200 KW motor full load current is about 370
amps and for 75% scale reading would be 500 amps.So your CT
rating would be 500/5 and the amp meter also of the same
rating.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / k.prakashchandra
Another method.Divide KW by 0.75 (lowest pf expected) to get
KVA. Calculate current which is about 380 A at 400 V line
voltage.You can choose a CT 0f either 400 or 500 A as
primary current.The secondary current of CT is decided by
meter and relays.This is generally either 1 or 5 A .
Is This Answer Correct ? | 1 Yes | 1 No |
how to ctrl motor by use of ac or dc drive.plz explain evdintly
in HVDC transmission system ,monopolar link has one conductor usually a negative polarity and use ground or sea return ?through negative polarity we could pass electricity or not yes means how it is possible
what is sinwave ups
anybody can give the voltage value for 1M ohm
how does oil cools the transformer
what is raw power & normal power
in how many ways we can make induction motor to run in reverse direction?
what is the role of energy meter in distribution system ?
how to calculate kA rating of device?
3 Answers Siemens, Vijai Electricals,
How to decide and select the different earthing wire size for the different types of earthing
what is difference between earth and ground?/
3 Answers Sree Rayalseema Green Energy Limited SRGEL,
how do we calculate contactor and fuse rating for a motor if its full load current is known,i want exact calculation for 1.5 kw motor????
1 Answers Allied Group, Nucon,