can we use the step down transformer to step up transformer
Answers were Sorted based on User's Feedback
Answer / sandeep m. parmar
yes a step down transformer can be used as step up if the
connections are reversed.
| Is This Answer Correct ? | 9 Yes | 2 No |
ya,its possible.. for ex: using a 11kv/415volt step down
transformer, in this primary voltage is 11kV and the
secondary voltage is 415volt(step down transformer)... now
we giving the input voltage to the 415volt side of the
transformer now the primary voltage is 415volt and secondary
voltage is 11kV(step up transformer).....
The step up and step down transformer is deponds upon
the input voltage is feeding side of the transformer(Primary
or secondary side)
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / lokeshraj
Yes we can use this in both step up and step down. But the
transformation ratio is not same in both case. It would be
slightly different.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sandeep m. parmar
yes i gave a short answer which is elaborated by Mr.J
Kartik. he is right.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / akatugba
On the issue of reversing step down as step up....Do you
ever put the 4poles into consideration..What now happen to
the grounding for protection, is the 4th pole for grounding
going to be on the 11kV outgoing? or on the incoming
415volts
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manoj
no, b'coz step up & step down t/f is design perposly,it
depend on wdg,for step down no of pri wdg more sec wdg
less,& for step up no of pri wdg is less & no of sec wdg is
more.
| Is This Answer Correct ? | 0 Yes | 8 No |
I have a shop heater with a 1/3 hp capacitor start, induction motor driving the fan. Intermittently, the fan motor speeds up significantly for several seconds (15-60 sec) then slows to normal operating speed. The manufacturer suggested changing the capacitor which made no sense, but I did it to no avail. Could this possibly be caused by the centrifugal switch intermittently reconnecting the start winding?
How many methods to take IR value of Current Transformer?
Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.
What is meant by system?
In Electrical 'Single Line Diagram' cable nomenclature shows "2 X 1C X 630sq.mm to be provided for one incomer. The question is how many cable to be proved for one Incomer.
HOW BETTER VOLTAGE REGULATION IS OBTAINED BY HIGH VOLTAGE TRANSMISSION....?
In case of delta/delta transformer if the one phase is blown out then what will be secondary line voltage ?
what is the formula to calculate voltage drop/loss on 66KV Transmission Line?
how to select the rating of neutral ct with reference to transformer secondary current(in power transformer,stepdown tansformer,for example2000kva,11kv/415volt
What is IGBT?Where it is used? What is the difference between IGBT and Thyristor?
5 Answers AC, Formo Plastic, HBL Power Systems, SECL,
. Why the transmission lines are in 11kV, 22kV, 33kv, and why not 10kV, 20kV, 30kV?
how to measure the dc current?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)