An 11kv system consisting of an underground cable to a sub
station about 300 meters away was shut down for about 10
hrs. On energising, it tripped off on earth fault about
10---20 mins later 6 times but since than it is not
tripping.its already 3 weeks now. The SPAJ was found to be
fine. what could be the cause.No test had been done to
determine the cause of the trippings till now because of
demand.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
If only you had replaced the breaker cubicle and test
charged you would have come to conclusion.If the all 3 poles
do not close almost at the same time and there is a time
gap, the breaker is likely to trip on EFR due to the
unbalanced current in case of 2 OCR + 1 EFR protection
scheme.In such cases it is advisable to test charge on no
load during the second time and confirm the mechanical fault
which is not consistent & does not occur always.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pillay
thanks but I had managed to ON the system and remained
energized with some load for a few minutes (10 -20 mins)
before it tripped again on earth fault , it happened 6 times
on (4/6/2011) and till today (13/07/2011) no problem. we
are using ABB spaj oc/ef relay.
Is This Answer Correct ? | 0 Yes | 0 No |
what will happen if 11KV is given to 1.5 square mm cable connected with constant load of 10A ?what will be the condition of cable after injecting the voltage?
Could anyone clarify my wondering. What is the difference between knee point voltage and saturation voltage of the CT. Is their any formula to calculate these values?
What do you mean by turns ratio of instrument transformer?
Difference between MCC and PDB
what is the voltage between the earth & neutral 2 is there any continuity TO BE between earth & NEUTRAL
why semicondoctor use in HT cable?
ynchronous M/C with under excitation with reactive power absorption , acts as a) synch. Motor b) synch gen c) synchr capacit
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
what is the instataneous value of voltage in a 3-phase balanced star connected circuit?
Wat is meant by OLTC?
LET ME NOW MORE ABOUT icu and ics for circuit breaker. how we calculate the rating of circuit breaker and i c u and ics values
Difference in load break switch, isolator and circuit breaker.