How can one improve linearity of an RTD based temperature
measurement system?
Answers were Sorted based on User's Feedback
Answer / guest
RTD has +/- 0.4% nonlinearity when used over 0 to 200 degC.
This is due to the relationship R= R0*(1+aT+bT^2). The
change in resistance for 0 to 100 degC is 38.5ohms for a
Pt100, while it is lesser at 37.3 ohms fro 100 to 200 degC.
Using a two slope method, one for 0 to 100 deg and another
for 100 to 200 degC, the linearity error can be brought
down from +/- 4% to +/- 0.1%.
Is This Answer Correct ? | 5 Yes | 3 No |
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
WHAT REASEAN USE TRANSMETER TWO WIRE & FOUR WIRE
What is the right procedure for adjusting the gap voltage of bently nevada vibration sensor?
what is upstream and downstream in liquid flow?
which type signal come control valve
wat are the interview questions asked in air india for post service engineer
1 Answers AirIndia, Shree Renuka Sugars,
What is hp & mp seperator .& what is its working principle ?
what is mean by hot loop and cold loop testing, whts different between both
What is difference between magnetic flow transmitter & Electromagnetic flow transmitter?
Can Any body tell me how to check Modbus Settings in ER300N L&T trivector meter?
What is Positive Calibration and Negative Calibration?
regarding level tx i would like to know how to select the range of the level transmitter in a closed drum(steam drum or deaerator)?