why used three wire in RTD.
Answers were Sorted based on User's Feedback
Answer / preeti
three wire connections can eliminate connection lead resistance effects from measurements
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / gomsy
third wire is used as lead wire compensation i.e it is
connected in parallel,hence effective resistence decreases
and will be helpful to calculate higher range of tempreture
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / santosh r apre
three wire connections can eliminate lead resistance from
mesurements.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / sam.r
Most RTD’s incorporate a third wire with resistance R3.
This configuration provides one connection to one end and
two to the other end of the sensor. Connected to an
instrument designed to accept 3-wire input, compensation is
achieved for lead resistance and temperature change in lead
resistance. This is the most commonly used configuration.
If three identical type wires are used and their lengths are
equal, then R1 = R2 = R3. By measuring the resistance
through leads 1, 2 and the resistance element, a total
system resistance is measured (R1 + R2 + RE ). If the
resistance is also measured through leads 2 and 3 (R2 + R3),
we obtain the resistance of just the lead wires, and since
all lead wire resistances are equal, subtracting this value
(R2 + R3) from the total system resistance (R1 + R2 + RE)
leaves us with just RE, and an accurate temperature
measurement has been made.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / seshu
The connecting wires long,resistance of wire changes as ambient temp fluccuates.to eleminate this problem we use 3 wire rtd
| Is This Answer Correct ? | 9 Yes | 10 No |
the RTD is
installed some distance away from the transmitter. Since
the connecting
wires are long, resistance of the wires changes as ambient
temperature
fluctuates. The variations in wire resistance would
introduce an error in the
transmitter. To eliminate this problem, a three-wire RTD is
used
| Is This Answer Correct ? | 2 Yes | 3 No |
how can you change unit of totalizer in siemens mag 5000 flow meter?
why we cant transmit the dc current easily
what is difference between total flow and flow rate in general ?? explain it with daily life example.
what is the difference between E/P positioner and I/P positioner in control valve , in which application the respective positioner are used in.
what is the difference b/w wet leg & dry leg level method
Why thermo wells are used?
principle of automatic votage regulator
what is written on orifice plate?
What is the reverse action and direct action
what is radar type level transmitters and its basic principle and how to calibrate it
What is the PLC Level & type.
2 Answers Bhushan Power Steel,
I have 475 hart communicator. this is not support any new type of instruments such as tranmitter,fieldvue DVC6200.DVC 200 since i got point out need to upgrade . my questions is how can upgrade new instruments software in my 475 hart communicator. can any answerplease>?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)