Answer / r k nair
Normal Cable Gland is also called Single Compression Cable
Gland. As the name suggests, while you tighten the gland,
the grip or compression is effected only at one p[lace
(i.e.) at the cable armour only. There is scope for
moisture and corrosive vapour to enter the gland and thus
into the cable.
Whereas in Double-Compression Glnad, the compression
happens both at the cable armour as well as at the inner
sheath. This is sort of two sealings. Hence, chances of
moisture or vapour entry are minimised. Hence these glands
are also known as Weather-proof cable glands or Flame-proof
cable glands.
Is This Answer Correct ? | 21 Yes | 1 No |
Answer / raffi
Single compression glands used for the unarmoured
cables.since you can make the grip only on cable sheath
whereas Double compression glands are used for armoured
cables as we can tight it with both cable inner sheath also
in cable armour.
Both glands can be used for exlosion proof areas, only
thing is that it should be certified for zone
classifications
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / sumith
single compression cable gland is used for normal panels and
it is not airtight.(it cant be used in flammable areas)
double compression cable gland is used for air tight panel i.e
purge panels(used in flammable areas)
Is This Answer Correct ? | 2 Yes | 6 No |
hii my name is sujith...i am preparing for HPVL GET 2010... so ,,,pls help me by send any previous questions or material to my site.....(Msujith_12@in.com) thank q
You are looking at the RS-485-side of an RS-232/RS-485 converter and the power supply voltage for the converter is +5V. Under idle conditions (no transmission), and assuming you have enabled the RS-485 output: what would you expect at: (a) Output A measured against output B (b) Output A measured against ground (c) Output B measured against ground
Galvanizing.
what is sil (safety integrity level
Hi buddies! my name is sachin and i am working as a electrical and instrumentation engineer in a paper plant. right now i am facing a problem and if someone could help me it will be an immense pleasure to me. i am using AC 800M to synchronise DCS500 drives on paper machine and rewinder.communication is on PROFIBUS and we are using NPBA-01 module to link profibus to DC drives.But these days two of these drives are showing a error named FIELDBUS COMM.TIMED OUT and the drives get tripped.I have changed the NPBA module and PROFIBUS cable.So if anyone can do please help me out with this problem.I'll be highly grateful.
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
Boolean algebra
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
why micro controller 8051/52's clock frequency is internally divide by 12 ?? and why it is further divide by 32 in UART serial communication ??
when the operation engineer told you that he gives the control valve order to open but there is no response ! what will you do ? and if you found that there is astuck , what will you do ? (note : it is apanumatic valve )
what is the difference between(Flame proof/Explosion proof)& Fire proof instruments.Both are same or different & if different in which way because the transmitter which have approved ATEX flame proof enclouser but it use PTPE O ring & PTFE Head Gasket,so its (fire safe/fire proof)????????
how to design orifice plate?what is the equation?