avr is an automayic voltage regulator ... it regulates
voltage before it synchronise with grid after
synchronisation it regulates power factor why....
Answer Posted / k.prakashchandra
It keeps the gen voltage the same at the set value
irrespective of variation in speed , load and grid voltage
after synchronization. It is useful whenever there is grid
failure as the gen speed suddenly increases to an extent
depending on the load interrupted.Then AVR does not allow
for rise in voltage.It is also very helpful while
synchronizing as you do not have to vary the excitation
every now and then ,once you have matched the voltages.If
you desire to keep the pf constant after synch and loading
,you have to switch over to APF mode from AVR ,both being
available with Auto channel.
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
what is sevice settings for mccb?How can be it setted?
After doubling voltage from solar cells & use step down voltage transformer can we get high current output with low voltage.
Why L.T.Cable voltage rating is 1.1kV,where as system voltage is 0.415kV?
What is d main advantage of using double circuit 3 phase transmission ?
What is tan delta & PPM in transformer? and whats its IS value?
what are the protecyion of transformer & generators
What is the tipical Online UPS input voltage for 20 KVA load ( 3 Phase or 1 Phase )? Why ? Explain it...?
What is mean by Sensitive Earth fault & what are the effects
8. A DYNAMOMETER TYPE WATTMETER RESPONDS TO THE.......
Give idea about General Engineering. From which book i can study this topic. Pl. reply me via email. My email is ravi@bhelhwr.co.in, also give the name of book/website, from where i can prepare it.
What are the three constants associated with a steady state error?
What should be the values of settling time, peak time, steady state error, overshoot, rise time, MPOS (Maximum percent over shoot) to keep the system in transient state, to keep the system in steady state ?
Do you need any help with FEWA Electrical Supervisor exams?
why the pf of semiconductor device is improved the electrical devices
what are the components in electrical control panel (for example: 415V, 3-ph, panel to operate utility and 3-ph DG set).