What is the out put of a CT? How the ratio is decided ?
Answer / mojinkoshy
The O/P of a current transformer (CT) is normally the secondary current of the CT. For eg.the CT may be rated like this "60/5A 15VA CL-1", in which 60/5A means the CT’s primary side current is 60A & the secondary side is 5A, 15VA means burden of the CT ie. Maximum power capacity / rating, CL-1 means the insulation class of the CT.
Since the O/P of CT’s are used for protection / measurement, the o/p rating is totally depends up on the ratio settings of the protective devices tripping capacity or that of the measuring instruments measurement capacity .
Is This Answer Correct ? | 5 Yes | 0 No |
what should be distance between phase to phase in 415v system?
How do we calculate over and under frequency tolerance from generator data?
Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it?
is the value of inductance depends upon the value of thitha in doubly excited machine??
We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.66 how can we maintane it? how can we balance our load?
why the transformer has no starter
why do we connect droop ct{in gensets}in y_phase only
why the air gap is necessary in the transformer core
why star point of HT motor not earthed?
what are upstream faults and downstream faults in power system
How can we do megger test of cable??
how to measure the current by compact digital equipment with dislay which fit inside any equipment