We have 250 KVAR cacitor bank & our average load is 200kva
but our power factor is average 0.66 how can we maintane
it? how can we balance our load?
Answers were Sorted based on User's Feedback
Answer / joseph
It is better to express the `Load' in kW. In your case it
is assumed that the average load at a P.F. of 0.66 is about
132 kW. Please note that excessive capacitors in circuit
can act as `Load'. Hence, firstly ascertain whether the
Power Factor is 0.66 lag (lesser capacitors than required)
or 0.66 lead (more capacitors than required). The best way
is to switch off all the capacitors for some time and take
the P.F., kW, KVA readings from your meter. Based on this
suitable solution can be provided.
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / ashish
Consider your load in kw i.e 200*p.f.=200*.66=132kw
Generaly capacitor bank used for improving power factor
then by using this formula kw & kvar relation formula. it
will help u to decide exact kavar for ur load.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / khalidshaikh
A CONSUMER HAVING TOTAL INSTALLED CAPACITY OR DEMAND UP TO
200 KVA. THE CONSUMER ARRANGED 250 KVAR CAPACTOR BANK, I
THINK CONSUMER IS MISS GUIDED OR HIS CONNECTION POINT IS AT
FOR DISTANCE FROM THE SUPPLY SOURCE, WHERE HE RECEIVE
DROPED VOLTAGE AND HIS LOAD IS TOTALLY INDUCTIVE WHICH
DECREASES POWER FACTOR. OR LEADING POWER FACTOR WHICH
CAUSES ALSO LINE LOSSES.
IT IS SUGGESTED THAT CONSUMER GOT INSTALL KVARH METER AND
KWH METER WITHOUT CAPACITOR BANK IN CIRCUIT THAN AFTER A
CERTAIN OBSERVATION TIME GOT CALCULAT POWER FACOR AND
ARRANGE FOR THE REQUIRED VALUE CAPACITOR BANK.
THANKS
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / zahid noor
Connecting a capacitor bank to laod is not sufficient to
control power factor, it is controlled by increasing &
decreasing value of capacitor on increase & decrease of
your load, which needs to be calculated & automatic control
can be given by APFC panels. Please contact a suitable
party .
Is This Answer Correct ? | 3 Yes | 2 No |
Which Programming software are use for Allen bradley PLC's?
Two electric lamps 40 W, 220 V each are connected in series across 220 V. What is the power consumed by the connection?
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
How to identify Motor leads in their order coming out from winding without tag (U1, V1, W1 & U2, V2, W2)?
when motor taking high amp what happen.
lorteny method
What is the following which is printed on electrical appratuses like AC21 ,AC 23 , etc ?
we all know that corona is nothing but ionization of air around the conductor and there by allowing current to pass through ionized air.but we are not getting any short circuit in between the respective phases though the air turned as a conductive media between them??
Why star pointed terminal have no current? how?
Did RMU have ct and pt ?
how we control the magnitude of a generator output
I want to know the 'Test voltage' for Tandelta testing of 3.3 / 6.6 / 11 KV Motors. Please explain