why transformers rating are in KVA
Answers were Sorted based on User's Feedback
copper losses depends on current and iron losses depends on
voltage. Total transformer loss depends on volt-ampere (VA)
and not on phase angle between voltage and current i.e., it
is independent of load power factor. That is why
transformer's rating is in KVA
| Is This Answer Correct ? | 33 Yes | 1 No |
Answer / parthipan
copper losses depends on current and iron losses depends on
voltage. Total transformer loss depends on volt-ampere (VA)
and not on phase angle between voltage and current i.e., it
is independent of load power factor. That is why
transformer's rating is in KVA
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / dinesh giri
Actully Transformer has any no its power factor.Its power
factor depends on the connected Load with it.The connected
load may be inductive or capactive or resistive Load or
mixed of all .
Connected Load rating in KW
As KVA*Power Factor(COS A)=KW
Rating of Transfarmaer is always taken in KVA
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mahender mohal
Simply transformer is a power transfer device not a power
consuming device,so it have negligible loss (depends on
volt-ampere),so cos$ is >0.96 approx. 1.P=vi;due to this
reason x-mer rating is in VA Or KVA.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / s. kumar
The power factor of the transformer depends on the load P.F
of the system where the transformer is connected. so the
manufacturer cant rate it in terms of KW.
| Is This Answer Correct ? | 1 Yes | 6 No |
how braking & making capacity of circuit breaker is calculated?
NGR? What is NGR?
Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
what is meant by frequency ?
why 3phase is 440v but where as we get phase voltage 220v,we have to get 220*3=660v.can u pleas give in detailed
What is system earthing?what are the types?
How many wall/floor flange will i use in bus duct system if we have in our design a 35th floor building.
How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer
what is the formula of high voltage testing of three phase induction motor?
What are the difference between these terms ? e.m.f, voltage, potential, potential difference, current etc? what are the difference between these terms ? (electromotive force) e.m.f, voltage, potential, potential difference, reference potential, reference potential difference, current. How can i explain and describe these all terms in single line each and little more explaination too thanks
how does high earth to neutral voltage affect electronic equipment?
how to measure earth resistance of a substation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)