How much ampere rating on LT side of distribution
transformer and also on HT side of 200KVA transformer
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
HT side 28 SWG (CR 12A,Fc 18 A), LT side 2 of 13 SWG
(combined CR 260 A, FC 590 A)or 6x 18 SWG (CR 270 A ,FC
616A) The currents in HT is 10.5A and LT 267 A f0r 200 KVA
Tr.CR=current rating,FC= fusing current
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / nirmit
Just Forgot HT LT here i give formula for amp
If 66000v KVA/114180*1000= found amp
11000v kva/19030*1000
440v kva/717.95
how
kva=route3*v*i
1.73*66000*i
114180*i
2000=114180*i
i=2000/114180
=0.0175*1000
=17.15 amp at 66000v
Is This Answer Correct ? | 5 Yes | 4 No |
single phase 230v three phase voltage 415volt why we aren't used line voltage 690v?
What is the function of an exciter in a generator?
What is the function of retrip in busbar?
when a machine act as genartor and as motor?
WHAT IS THE PARTIAL DISCHARGE TEST?
What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?
0 Answers Anglo Platinum, Narnarayan Electrical,
What size cable is used for HT cable to the transformer of 630kVA, and the supply voltage is 11kV
Name different types of circuit breakers and their voltage ratings?
In AC Drives How can change & control its output Frequency?
does over charging of a battery reduce its life?
As per which Indian Standard induction motors are manufactured?
why plc need seprate earthing?