WHAT IS B & C CLASS SURGE PROTECTION AND WHAT IS DIFFERENCE
BETWEEN B & c CLASS SP
Answers were Sorted based on User's Feedback
Answer / dhiraj banka
Class b SPD is for lightning surges & class c SPD is for switching surges.Class B+C protects both from lightning & switching surges.
Is This Answer Correct ? | 8 Yes | 3 No |
For surge arrester (lighting arrester) class defines the
capacity of energy can dissipate by SA.
Class in generally not defined by B & C but it defined a
class 2 , Class 3 , Class 4 & class 5 for sub stations.
For 145 kv (110,132 kv ) class 2
For 400 kv ( 400 kv) class 3
For 540 kv (generally not use in india) class 4
For 765 kv Class 5
Is This Answer Correct ? | 6 Yes | 3 No |
SUPPOSE A CIRCUIT BREAKER HAS TRIPPED THE THE LINE WHEN A FAULT OCCUR ON IT.NOW WHEN THE FAULT HAS BEEN CLEARED, HOW THE CIRCUIT BREAKER WILL CLOSE AUTOMATICALLY NOT MANUALLY.
6 Answers Bureau of Energy Efficiency, DVC,
what is alternator?
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?
Why we are putting off the APFC(automatic power factor control) panel while the generator is running?
how to syncronize two dg sets
what will be the magnetizing current in the testing of 27 MVA transformer?
which type of starter is suitable for single phase motor ?
what is a starter ??
how to calculate generator capacity?(kva)
If only R Phase is connected in 2 pole elcb, n is not connected than it will work or not in ground fault.
In all the generators, the excitation supply is DC. What is the significance of DC excitation? What will happen if AC supply is given as excitation supply?
Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required
9 Answers Emerson, Rajshree Sugars, Siemens,